ECN Forum
Posted By:
sparkync
uf cable near pool
-
03/23/07
12:55 AM
As long as I stay at least 10 ft. away from the wall of the pool, can't I run uf cable to post lamps around the pool? Thanks Steve...
Posted By:
George Little
Re: uf cable near pool
-
03/23/07
01:31 AM
I say you only have to stay 5 feet away from the pool per 680.22(B). UF wire could be installed at least 12" deep and GFCI protected if you can satisfy 300.5 T.300.5 Column 4.
Posted By:
sparkync
Re: uf cable near pool
-
03/23/07
01:39 AM
Thanks George, I don't know where I got the 10ft. at.. Steve..
©