Doing a job adding some circcuits for parking lot lights. One of the underground circuits has pvc run to one of those green rectangular underground boxes (with no bottom) and wires spliced in it, in and out. This can't be legal.
Posted By: Roger Re: underground boxes - 03/20/07 05:06 PM
Aldav, this is a common installation and is allowed per 314.30(C)

Quote
(C) Handhole Enclosures Without Bottoms Where handhole enclosures without bottoms are installed, all enclosed conductors and any splices or terminations, if present, shall be listed as suitable for wet locations.
Roger
Posted By: HotLine1 Re: underground boxes - 03/20/07 06:58 PM
Just a thought, does the cover indicate "Electric" ???
The green 'irrigation' don't exactly fly, as they are intended for 'low voltage' circuits.

John
Posted By: Roger Re: underground boxes - 03/20/07 08:04 PM
Good catch John, I was thinking Quasite type boxes.

Roger
Posted By: HotLine1 Re: underground boxes - 03/20/07 09:27 PM
Roger:
I had to read it twice.
Thanks for the compliment!
John