Posted By: George Little Pull Box v. Junction Box - 11/11/06 05:21 PM
If I have 2 inch conduit entering one side of a box and exiting with a 2 inch directly across from the conduit entering the box we have a straight pull. Right? If the conductors are AWG #4 or larger the box needs to be at least 16 inches between conduit entries hence at least a 16 inch box. (NEC 314.28(A)(1) '05 Ed.) Now- if I splice these conductors can I reduce the size of the box to 12 inches based on (2)?

Edited for spelling [Linked Image]

[This message has been edited by George Little (edited 11-11-2006).]
Posted By: resqcapt19 Re: Pull Box v. Junction Box - 11/11/06 06:36 PM
George,
A splice doesn't change anything. If the conduit goes straight it is 8 X and if the conduit goes out a wall at 90° it is 6 X.
Don
Posted By: George Little Re: Pull Box v. Junction Box - 11/11/06 07:26 PM
Don- I agree with you put you'll get arguements if the conduits are offset or if there is a splice. I think it should be made clearer somehow. I ask for a 16 inch box.