Wasn't there a rule or maybe a proposal to have the outlet for a hood over a residential kitchen range on a separate circuit? Can't find it.
Posted By:
George Little
Re: Kitchen Hood Outlet
-
09/17/06
03:23 AM
I found the code reference I was looking for and it appears that the connection of a range hood is permited to be cord and plug and if so it must comply with 422.16(B)4. Other than that it muist be hard wired.
Posted By:
HotLine1
Re: Kitchen Hood Outlet
-
09/17/06
04:09 PM
George:
20 min to find your answer???
Just messing with you!
John
Posted By:
ShockMe77
Re: Kitchen Hood Outlet
-
09/19/06
02:10 AM
What a coincidence!
From Mike Holt's monthly NEC Questions and Answers e-mail:
Quote
Q10. Am I required to have a dedicated circuit for an above the range microwave that includes a range hood if it’s cord-and-plug connected?
A10. Yes, see 422.16(B)(4)(5).
Posted By:
gfretwell
Re: Kitchen Hood Outlet
-
09/19/06
03:53 AM
IAEI also fielded a question that answered, a range hood is not auxillary equipment to the range.
©