Posted By: watersparkfalls identification - 08/22/06 06:08 AM
is 200.6 ment that you cannot re-identify a colored conductor(black,blue,red,ect...)smaller than #6 in pipe
to a grounded conductor using white tape???

thanks,
H20
Posted By: resqcapt19 Re: identification - 08/22/06 11:27 AM
yes
Posted By: cpal Re: identification - 08/22/06 11:56 AM
I agree with Don
and it is done all the time


Charlie
Posted By: watersparkfalls Re: identification - 08/22/06 01:21 PM
thanks,

H20
Posted By: renosteinke Re: identification - 08/22/06 01:42 PM
I'm not at all sure that this wording in the code was deliberate. I agree, technically re-identifying a wire to make it white is not allowed.

Personally, I disagree with this rule. Argument aside, not a single supply house here carries #6 or #8 wire in any color but black. Ironically, sometimes the box dtores do!

Frankly, I am simply delighted when ANY attempt is made to properly identify conductors.
Posted By: JBJQEP Re: identification - 08/22/06 02:17 PM
Amen to any attempt to identify the conductors. It seems to be too much trouble to go the extra foot to properly identify conductors when their purpose is not clearly demonstrated or seen.
Posted By: gfretwell Re: identification - 08/22/06 03:37 PM
I think the box stores carry colors because a homeowner is more likely to buy cut wire in these sizes. They also need the help to avoid confusion. Although I have seen pros who should know better get wires misidentified.
Boom!
Posted By: macmikeman Re: identification - 08/22/06 05:05 PM
Simple personal opinion is it wouldn't be a bad idea to change the minimum size allowed to number 8. #10 and below is pretty common stuff on the shelves. The rule apears to have been written with big shops in mind. The ones that will carry lots of inventory. Time for an old quote from the past " Its the economy stupid"
Posted By: cpal Re: identification - 08/22/06 11:26 PM
The rule apears to have been written with big shops in mind. The ones that will carry lots of inventory

I would be more inclined to believe it is the wire mfg that drive these types pf code issues, if all the mfg stopped making white insulation for 8AWG and 6AWG the languge would change.

Just a thought


Charlie
Posted By: George Little Re: identification - 08/23/06 02:31 AM
You guys want some cheese with that whine?

[This message has been edited by George Little (edited 08-22-2006).]
Posted By: resqcapt19 Re: identification - 08/23/06 11:57 PM
You can get white up to at least 500kcmil. There have been proposals to require the use of white insulation for all sizes of grounded conductors. These proposals along with the ones to permit re-identification of smaller conductors have been soundly rejected by the code making panel.
Don