low voltage splice accessibility
-
06/22/06
12:44 AM
I need to splice a 2 wire #18 thermostat wire. Does this spice need to be accessible? This is in a garage that is going to have a fire rated ceiling installed over the splice.
Posted By:
Ron
Re: low voltage splice accessibility
-
06/22/06
02:26 AM
Although the code doesn't require the splice to be in a box or remain accessible, it is a darn good idea.
Posted By:
HotLine1
Re: low voltage splice accessibility
-
06/22/06
02:52 AM
As Ron said...
the 'Code' of common sense' should prevail, and the splice should be accessable.
Think about if you may have to return!!!
John
Posted By:
mister h
Re: low voltage splice accessibility
-
06/22/06
03:02 AM
A nail on box and a blank cover ($ 1.50)
would be worth it
©