Posted By: George Little Bonding per 680.26(C) - 06/05/06 12:02 AM
Are the lugs and screws that are installed on pool & spa equipment by the factory suitable for bonding the equipment to the bonding grid? Do inspectors ask that the contractors replace these lugs and screws with ones made of stainless steel, brass or copper or other non-corrosive material?
Posted By: Larry Fine Re: Bonding per 680.26(C) - 06/05/06 01:39 AM
Yes, and they shouldn't.
Posted By: HotLine1 Re: Bonding per 680.26(C) - 06/05/06 10:20 PM
George:
I have to agree with Larry
Yes, and why are they requested/required to be replaced??

John
Posted By: George Little Re: Bonding per 680.26(C) - 06/06/06 01:15 AM
John & Larry- I agree with you guys and so does UL. Once you start altering a UL Listed equipment you are inviting problems. The equipment is Listed with the lugs on it and that's where we connect the Bond wire. But, we still have some inspectors out there that read the wording about brass, copper or stainless connections and they have the contractors changing them. I say they are wrong for doing so.
Posted By: HotLine1 Re: Bonding per 680.26(C) - 06/06/06 10:09 PM
George:
Perhaps it's time for a little CE or Seminar on Article 680??

Only mention of the SS, Brass of Cu lugs that I'm aware of regards bonding IG???

Maybe I missed something??

John