Posted By: shortcircuit Mass 2005 revisions - 02/17/05 11:35 PM
334.12(A)(2)(as revised by Mass) allows the use of romex above suspended ceilings in other than dwellings.

300.11(A)(2)(as revised by Mass) says...

Nonfire-Rated Assemblies. Branch-circuit wiring associated with equipment that is located within, supported by, or secured to a suspended ceiling that is not an integral portion of a fire-rated floor/ceiling or roof/ceiling assembly shall be permitted to be supported by the ceiling support wires.


So does this mean that we can run romex above a dropped ceiling , supported by the ceiling support wires, if the ceiling is not a fire-rated assembly?

shortcircuit
Posted By: iwire Re: Mass 2005 revisions - 02/19/05 12:28 PM
Sure does.
Posted By: tkb Re: Mass 2005 revisions - 02/22/05 10:26 PM