Posted By: watersparkfalls triplex/urd - 03/06/06 06:29 AM
what is the lettering for triplex or as its called out here in the west coast "URD"?
a contractor(general)has poured the foundation for a house and ran 2 1/2" pvc under his garage slab and up into a interior wall in the garage (remote meter)
well now the home owner wants electric heat and electric insta heaters for tub and kitchen, which the original 200 amp service wont handle (has a comp with a high locked rotor current) and now they want to bump up to a 400 amp servic(320 amp meter no doughnuts or ct can)but problem being one 2 1/2" pipe.
will the 4/0x4/0x2/0 pair fit? not that it will be an easy pull mind you. i dont like what he is suggesting and depending on actual lettering of triplex will determine if it is even legal. when i tried to suggest putting service on exterior wall he just about blew a gasket. another problem is running though one panel to get to another ive never done this and wonder if a gutter below both panels will be required?

thanks,
h20
Posted By: XtheEdgeX Re: triplex/urd - 03/06/06 04:32 PM
Legally, you can put up to 7 #4/0's in a 2 1/2" conduit. That's with an insulation suitable for a damp or wet location.
I've never seen triplex installed underground. Someone else may be able to correct me on this, but since the neutral conductor is not insulated, you may not be able to use it this way.
You are also not allowed to use the panel as a junction box to get to the other. 312.8 in the NEC prohibits this.
Posted By: Tiger Re: triplex/urd - 03/06/06 07:14 PM
Article 312.8

"...unless adequate space for this purpose is provided."

Dave
Posted By: XtheEdgeX Re: triplex/urd - 03/07/06 02:17 AM
I've not seen a panelboard yet that had adequate space provided.
Posted By: Tiger Re: triplex/urd - 03/07/06 03:09 AM
I'm just pointing out that you CAN use the panel as a junction box. You have to figure the available space and calculate if the splices would comply or not.

Dave
Posted By: caselec Re: triplex/urd - 03/07/06 03:36 AM
XtheEdgeX, why don't you feel that most panelboarsd have don't have space? I think that it would be very hard to exceed the allowable gutter space in most situations. In this case I could see more of a problem because of the wire size. I think wire bending space is going to be a bigger issue.

H2O, will the conductors from the remote meter be service conductors or feeders? (will there be overcurrent protection at the meter)

Curt
Posted By: watersparkfalls Re: triplex/urd - 03/07/06 04:38 AM
triplex is sorta a generic term we used back in mn. it isnt a bare neut(guy wire)it is 2-4/0's with a insulated neutral.
guess thats why they call it urd here in the west coast.
thanx guys appreciate the comments.

h20
Posted By: e57 Re: triplex/urd - 03/07/06 07:42 AM
Never heard of URD.... (On the west coast) googled it and came up with mostly med. voltage cable. (KV) You're right though, "Triplex" is pretty generic, and means diferent things to people. I think of it as arial service drop wire. "Triplexed", would be concentric clockwise twisted conductors in my mind.

Anyway you would have more room than you need to pull 3 4/0....(yes it won't be easy with distance and bends) Unless you are dealing with POCO rules like PG&E. You might be looking at 4"....
Posted By: XtheEdgeX Re: triplex/urd - 03/07/06 05:53 PM
You CAN NOT use a panelboard as a junction box.
NEC 110-3(b) Installation and Use. Listed or labeled equipment shall be installed and used in accordance with any instructions included in the listing or labeling.
UL-67, to which panelboards are tested listed and labeled, does not list a panelboard to be used in this way.
Here is an interesting read on this subject, that includes a response directly from UL. http://www.isa-home-inspections.com/articles/tecspk08.pdf
Posted By: George Little Re: triplex/urd - 03/07/06 08:52 PM
XtheedgeX- I hope that your not saying what it looks like your saying because there are a bunch of panels out there with splices in the gutter space. I don't think UL will ever say that this panel is listed for allowing splices in the gutter space. BUT- the code is rather clear that you can splice in enclousures with overcurrent devices in them if you have the room and stay within the percentages called out. The words "Listed for the purpose" with respects to splicing are not found here. I'm wondering how we measure the 75% or 40%. I venture to say if you asked a pointed question of UL about "Listed for splicing" they will always say "No it's not Listed for splicing". Probably no manufacturer has ever submitted a producted and specified that it be Listed that way because the code doesn't ask that it be so Listed for splicing.
Posted By: Fred Re: triplex/urd - 03/07/06 10:35 PM
"Triplex" or "Quadriplex" are generic terms to describe a wire assembly of 3 or 4 conductors. Underground Triplex or Quadriplex are called URD around here and all of the conductors are insulated and listed for direct burial. Overhead tri/quad plex has an uninsulated grounded conductor and is called ACSR which stands for Aluminum Cable Steel Reinforced and is not listed for direct burial. I didn't realize URD was a regional term. I believe the correct term for the insulation type which is listed for direct burial is USE.
Posted By: earlydean Re: triplex/urd - 03/07/06 10:46 PM
I always thought URD insulation was similiar to USE. If so, be careful, as USE conductors cannot be installed indoors, as the insulation will emit toxic fumes.
Posted By: resqcapt19 Re: triplex/urd - 03/08/06 12:37 AM
XtheEdgeX,
The UL statement is in conflict with the CMPs published statements in the ROPs and ROCs on this issue. Also if the gutter space in a panel is not listed as a "wireway" there is no way to make the connections to the OCPDs.
Don
Posted By: XtheEdgeX Re: triplex/urd - 03/08/06 02:28 PM
George Little - Although I don't think splicing is allowed in a panelboard, that is not what we're talking about here. We're talking about using a panel as a junction box and pulling a feeder through it to get to another panel. And FYI, there are lots of items on the market that are UL listed for splicing.
resqcapt19 - C'mon. You're just picking apart my reply now. Of course the panel is a wireway for the OCPD's. But not for wiring to go through the panel to get to another.
I think we just have a few here trying to defend this because they do this. I also think it's pretty lousy workmanship to pull wire through a panel like it's a junction box, and to splice wire in panels, instead of laying the job out correctly to avoid this.


[This message has been edited by XtheEdgeX (edited 03-08-2006).]
Posted By: resqcapt19 Re: triplex/urd - 03/08/06 06:42 PM
XtheEdgeX,
Quote
C'mon. You're just picking apart my reply now. Of course the panel is a wireway for the OCPD's. But not for wiring to go through the panel to get to another.
I am picking apart your reply because it is in conflict with the published statements of CMP 9. The code making panel clearly intends that you can use the panel wireway for external conductors. If it is a wireway for the panel conductors, it is a wireway for all condcutors up to the fill requirements in the code section.
Quote
I think we just have a few here trying to defend this because they do this.
No, I don't do this, but it is permitted by the code.
Quote
I also think it's pretty lousy workmanship to pull wire through a panel like it's a junction box, and to splice wire in panels, instead of laying the job out correctly to avoid this.
I agree that it is poor workmanship, but again, it is code complaint.
Don