Posted By: SparkyDave Electrical Panel In One Hour Rated Wall - 03/02/06 04:14 PM
Is it allowed in the NEC to install a loadcenter in a one hour fire rated wall? I have been looking thru the NEC and haven't found anything regarding this as of yet. If it is not allowed, could someone provide me with the article number.

This loadcenter is for one of the units in a highrise multifamily residential project that we are doing. All the other units in the building didn't have this concern, however, this one unit does not have any walls that will really accept the loadcenter. Asthetically that is.

Thanks for any help

Dave
Posted By: Roger Re: Electrical Panel In One Hour Rated Wall - 03/02/06 05:11 PM
Welcome to the forum Dave.

With the exception of some basic wording in 300.21, this is not an NEC issue.

NFPA 221; "Standards for Fire Walls and Fire Barrier Walls" would be helpful.

A UL design would be needed and can be found in the UL Orange books (Fire Resistance Directory) or go to this UL page to start a search, but it can be frustrating unless you know what you're looking for.

The easiest way to do this would be to "five side" the panel with 5/8" sheetrock, this would mean the wall would have to be atleast a 6" deep wall.

Roger
Thanks for the quick reply. I had found that article and only that article in the NEC that pertained to my question. Just wanted to make sure before I went on with this project.

Thank you for the welcome also.

Dave
A panel in a fire wall..a wall that depends upon both facings for its' rating....would most certainly cease to be effective. A common method of dealing with this is to "box in" the panel; that is, surround it with several layers of sheetrock.

The question comes down to "what is the specific wall design?" There are various "Fire Resistance" directories out there that detail different wall types, and their ratings. You would have to find your wall in one of these in order to determine what you need to do.

"But Steel doesn't burn" ....someone is sure to say. True enough, but steel does get hot. For a wall to pass a "fire test," not only must the wall survive, but the side away from the fire is not allowed to get hot either.
Posted By: sandsnow Re: Electrical Panel In One Hour Rated Wall - 03/03/06 03:49 PM
I have not found anything in our building code or in the UL direstory for fire resistance that allows for panelboards in fire resistive construction.

Rodger's method of "five siding" is commonly accepted, but is not backed up by any tested assembly I've seen.

If anybody has a UL classified (or equal) assembly for this I would really like to see it.
Posted By: Roger Re: Electrical Panel In One Hour Rated Wall - 03/03/06 05:47 PM
Larry, by "five siding" the enclosure you are simply contouring the membrane around the enclosure unbroken, so the only concern would be the conduits penetrating through the sides which would need to be sealed properly.

In otherwords, the enclosure could be removed and you would simply have an indentation in the wall that would not compromise the thickness of the overall membrane(s).

With this being said, IMO there really is no need for a designed assembly.

Once we go above a 2 hour wall design things would be different

Roger
Posted By: eprice Re: Electrical Panel In One Hour Rated Wall - 03/03/06 11:01 PM
Quote
In otherwords, the enclosure could be removed and you would simply have an indentation in the wall that would not compromise the thickness of the overall membrane(s).

As has been said "five siding" enclosures is a commonly accepted approach, however, it is not only the thickness of the membranes, but the the thickness of the space between them that enables a wall to hold up to a test. Depending on the size of the panel, placing it in the wall may cause a localized area where stud support for the sheetrock is spaced farther apart than what was tested by UL. As sandsnow stated, there is no test data that backs up the use of "five siding" to solve these situations

For me, a factor that would weigh in to determining the acceptability of this approach would be, what is the reason the wall is rated? In the IBC for example, some walls, such as stair enclosure walls and exit passageway walls (these are more than just corridors) get special treatment. These are required to have no penetrations except for wiring, ducts, etc., that are needed to serve the enclosure or exit passageway, and that would include both membranes of the wall. I would be very reluctant to allow a panel, even with "five siding", in one of these walls. The wall assemblies were not tested by UL with an indentation. In other rated walls, I would be more inlined to accept the "five siding" approach.
Posted By: Roger Re: Electrical Panel In One Hour Rated Wall - 03/03/06 11:25 PM
Eprice, if a wall design or code specifically prohibits a panel, outlet, Fire Extingisher Cabinet, or any other item from being installed in a particular wall, then that is a different story as was noted in the last sentence of my post.

We are now moving into other areas from the original question concerning a "one hour wall". In most one hour designs the required double 5/8" sheetrock can be on one side of the wall if desired.

Roger
First of all, nobody can speak for UL except UL itself.

That said, one of the services UL offers is a field review of modified assemblies, where a decision is made as to whether the item continues to meet UL's standards, without requiring additional testing.
The reason for this service is two-fold:
-First, sciensc, and logic, allows us to make such decisions wisely, assuming we have the necessary data; and,
-It is simply not possible to test every possible variation of a wall.

The issue is one of "engineering judgement." An AHJ really doesn't have a leg to stand on if his 'instincts' conflict with the professional judgement of the engineer or architect.

If there's a question, then it is time to make the engineer earn his pay, and have him make the call.
Fire rated walls are engineered assemblies but there are, what amounts to, mastered plans for firewalls. I would be surprised if there isn't a "master" for a wall with a pocket in it big enough for a panel. This can't be the first time it has come up.
Posted By: sandsnow Re: Electrical Panel In One Hour Rated Wall - 03/06/06 05:33 AM
Rodger
Do you have a reference for two layers of 5/8 on one side of the studs being identified in an UL or ICC assembly?
Posted By: Roger Re: Electrical Panel In One Hour Rated Wall - 03/06/06 02:48 PM
Larry, I'll see what I can find today.

Roger
Sandsnow, the UL "Fire Resistance Directory", Volume 1, contains a very large number of common construction methods, and their respective fire ratings.
Unfortunately, this book has no index, so you must plow through it until you find something similar.

The design UL designates as "U432" is a simple wall, faced with gypsum board on both sides, and supported by steel studs 24" on center. The cavities are filled with fiberglass insulation. Even theough the gypsum board is only a single layer of 5/8" on each side, this design has a 1 hr. fire rating.
Design "U 425" is similar, but also contains supplimentary information detailing what must be done to obtain different ratings. Under this design, a double layer (both sides) of 5/8 results in a two hour rating for the wall.

From this, and other designs, it is reasonable to equate a double layer of 5/8" gypsum board, on it's own, as equating an hours' worth of fire resistance at that point.


Now- for our panel installation....as I see it, by creating a lined "pocket" in the wall, you are actually moving the panel "outside" the wall. Even though the panel may sit flush with the face of the wall, the wall actually "goes around" the panel. Conduit going through this "pocket", into the panel, is no different than a pipe exiting through the top plate of the wall, and should be treated in a similar manner.
Posted By: sandsnow Re: Electrical Panel In One Hour Rated Wall - 03/07/06 04:14 AM
reno
You describe pretty much how the installation of a panelboard in a fire resistive wall was arrived at and justified by numerous jurisdictions.
No test data to back it up. Check out design A202 for ceilings. The luminaires are identified and so are the protection methods. A fire resistive wall assembly would include the panelboard if it was evaluated with it installed.
So why isn't a panelboard shown in the wall assemblies?? Simple. No one has ever asked that it be evaluated or they did and it didn't pass.
Sandsnow, I'm not sure what you are referring to. Design A202 meerly says "UL listed type fixtures"...not any particular fixture, or specially rated fixture. It then follows that the fixtures are not to ocupy more than 24% of the ceiling. Nor are the fixtures wrapped in gypsum.

Your analogy is flawed. Even if it were to be applied....we would be left with "UL listed panels" taking up no more than 24% of the wall.

I have performed numerous ANSI fire tests of building assemblies. I have seen numerous variations of standard assemblies compared to the basic assembly. There is simply no basis to your assertion that either the tests were never done, or that they were, and failed.

For example, while I have not seen fire-rated walls evaluated with panels in them- I have seen the tests done with ATM machines poking through. Since ATM machines contain "fire safes", there is some basis to condsider them as analogous to a panel wrapped in gypsum. In those particular tests, the firewall retained its' integrity.

I think it is safe to assume, after more than a century of systematic testing of firewalls, that were there a problem with "wrapped" panels in firewalls, it would have been documented by now.
Posted By: eprice Re: Electrical Panel In One Hour Rated Wall - 03/07/06 05:05 PM
Quote
In most one hour designs the required double 5/8" sheetrock can be on one side of the wall if desired.


I have to disagree. I have looked through many of the descriptions of tested assemblies on the UL web site and in the Gypsum Association's Fire Resistance Design Manual. I can find nothing to support your statement. All of the desgins show the placement of the various elements of the assembly and event get into details such as how the joints are to be staggered on oposite sides of the wall.

This statement from UL is informative (It is on the page you linked. Scroll down to part II General):

Quote
Fire-resistance ratings apply only to assemblies in their entirety. Except for those separately rated structural members supporting tested assemblies, individual components are not assigned a fire-resistance rating and are not intended to be interchanged between assemblies but rather are designated for use in a specific design in order that the ratings of the design may be achieved.

All ratings are based on the assumption that the stability of structural members supporting the assembly are not impaired by the effects of fire. The extent of damage of the test assembly at the rating time is not a criteria for the rating.

From this I gather that rated assemblies are like listed equipment. If you modify them, you no longer have the same thing that was tested. It is not the two layers of sheetrock that give the assembly its rating, but rather, the assembly as a whole. The quote also points out that the stability of the structural members supporting the assembly must last at least until the end of the rating time. If both layers of sheetrock are moved to one face, a fire from the opposite side will immediately begin to degrade the stability of the studs. Such an assembly would certainly not perform as well as the originaly tested assembly.

Having said all of this, I do believe that placing a typical flush mounted panel in a rated wall by "five siding" it, is a commonly accepted practice, and is a modification of a rated assembly that could be allowed by the AHJ, based on the belief that it will not have an adverse effect on the performance of the assembly.

As I pointed out in my previous post, there are rated walls used for specific purposes in which the code specifically prohibits penetrations. In these cases, I feel that the panel installation would not be acceptable. I only mentioned this, because the OP was a general question about placing panels in rated walls, and I wanted to bring out this factor that would effect the answer to that question in some scenarios.


[This message has been edited by eprice (edited 03-07-2006).]
Posted By: Roger Re: Electrical Panel In One Hour Rated Wall - 03/07/06 05:52 PM
Eprice and Larry, you are correct that it is the assembly as a whole, and I agree that my statement is not backed up by any specific design.

However, the thickness of the membrane is what defines the rating of the protection, for an example, see wall type U424, although it is an exterior wall the protection is described as "Wallboard Protection on Interior Side of Wall" and list the layers needed to provide the required protection for the rating.

Eprice, I think this is the link you were posting.

Roger
Posted By: eprice Re: Electrical Panel In One Hour Rated Wall - 03/07/06 06:30 PM
Roger,

U424 actually supports my argument. If you look at the design sheet, it tells you that it is tested for exposure to fire from the interior face only. That assembly does not have a fire rating for exterior exposure and could only be used in those cases where the code only requires a rating for fire exposure from the interior face. Where the distance to a property line is greater than 5 feet, IBC section 704.5 only requires a fire rating for exposure from the inside. Those are the cases where U424 could be used.
Posted By: Roger Re: Electrical Panel In One Hour Rated Wall - 03/07/06 07:10 PM
Eprice, I agree. My point is that two layers of 1/2" sheetrock (in this case) on the interior provides a one hour barrier from the other side of the membrane.

I do agree that if the protective membrane is only on one side of the wall, the structural components of the wall are not protected and in turn would compromise the whole assembly.

Roger
Posted By: sandsnow Re: Electrical Panel In One Hour Rated Wall - 03/08/06 03:04 AM
reno
the installation of the luminaires in the assembly is a modification to the assembly just like the installation of the panelboard. The difference is in this case there is a provision for the installation of the luminaires.

"There is simply no basis to your assertion that either the tests were never done, or that they were, and failed."
What other possibility is there?? I ve not inquired as to why the panelboard is not identified in the assembly. I have asked about other items. The answer is always it s never been submitted or it can't pass the test.

"I think it is safe to assume, after more than a century of systematic testing of firewalls, that were there a problem with "wrapped" panels in firewalls, it would have been documented by now."
I would think that if it had been tested with the panelboard in the wall and found acceptable, it would be mentioned in the assembly.

"For example, while I have not seen fire-rated walls evaluated with panels in them- I have seen the tests done with ATM machines poking through. Since ATM machines contain "fire safes", there is some basis to condsider them as analogous to a panel wrapped in gypsum. In those particular tests, the firewall retained its' integrity."
That is the start of some basis to accept the panel in an assembly. was the steiner tunnel test where they heat it up and then hit it with the hose when they take it out? Is there any documentation as far as the results of this test?

Here is what the UL guide info is on design modification:

Design Modifications
Careful consideration needs to be given to alterations or modifications of the fire resistance assemblies.

When field issues arise, it is recommended the first contact for assistance be the technical service staff provided by the product manufacturer noted for the design. Users of fire resistance assemblies are advised to consult the general Guide Information for each product category and each group of assemblies. The Guide Information includes specifics concerning alternate materials and alternate methods of construction.

My opinion is that the panelboard wrap would pass if it were tested, but am in no way a qualified expert to make that assertion.