Posted By: kens gfci in unfinished basement - 01/10/06 03:11 PM
opinions, a dedicated recp for a freezer in unfinished basement gfci or not
thanks,
ken
Posted By: gfretwell Re: gfci in unfinished basement - 01/10/06 03:21 PM
210.8(A)(5)ex2 ... as long as it is a single receptacle and there is an accessible GFCI receptacle in the basement

[This message has been edited by gfretwell (edited 01-10-2006).]
Posted By: harold endean Re: gfci in unfinished basement - 01/11/06 01:37 AM
I don't think a GFI would be good for a freezer or refrig. Too much chance of a false trip and spoiled food. Like Greg said, make it a single, don't give it access and I don't think you will have a problem.