Posted By: shortcircuit Lightbulb Clearance - 12/06/05 12:39 AM
Is there a code requirement for the distance that a incandescent type A-lamp would be required to maintain from combustible surfaces such as wood?

For instance, if a 60watt A-lamp, screwed into a keyless lampholder in a basement of a dwelling, was within an inch of a wooden rafter, this would seem to be a hazard.

410.5 gives me some guidance, but is there any other clear guideline that would specify distances from combustible material for type A-lamps?

shortcircuit
Posted By: renosteinke Re: Lightbulb Clearance - 12/06/05 01:35 AM
Depends on the bulb used...do you have a thermocouple handy?

If I remember correctly, industry standards set 140 degrees F as the maximum temperature a fixture can cause on a "flamable" surface.
Posted By: e57 Re: Lightbulb Clearance - 12/06/05 02:17 AM
"within an inch of a wooden rafter, this would seem to be a hazard." - Yep....bulb to the side or below, I think it would be too close.
Posted By: jwhite Re: Lightbulb Clearance - 12/06/05 03:00 AM
410.5 Luminaires (Fixtures) Near Combustible Material.
Luminaires (fixtures) shall be constructed, installed, or
equipped with shades or guards so that combustible material
is not subjected to temperatures in excess of 90°C
(194°F).