New CA NEC (CEC) gas rules? - 09/28/05 06:06 AM
Old...
New...
Anyone have a copy of the 2004/5 CEC to know if this got changed to the 2002 wording? Are we still bonding gas to the GEC?
Quote
250.104(b) Metal Gas Piping. Each aboveground portion of a gas piping system upstream from the equipment shutoff valve shall be electrically continuous and bonded to the grounding electrode system.
New...
Quote
250.104(B) Other Metal Piping. Where installed in or attached to a building or structure, metal piping system(s), including gas piping, that may become energized shall be bonded to the service equipment enclosure, the grounded conductor at the service, the grounding electrode conductor where of sufficient size, or to the one or more grounding electrodes used. The bonding jumper(s) shall be sized in accordance with 250.122 using the rating of the circuit that may energize the piping system(s). The equipment grounding conductor for the circuit that may energize the piping shall be permitted to serve as the bonding means. The points of attachment of the bonding jumper(s) shall be accessible.
FPN:Bonding all piping and metal air ducts within the premises will provide additional safety.
Section 250.104(B) was revised for the 2002 Code to state that gas piping is treated exactly the same as all "other metal piping" systems within a building.
FPN:Bonding all piping and metal air ducts within the premises will provide additional safety.
Section 250.104(B) was revised for the 2002 Code to state that gas piping is treated exactly the same as all "other metal piping" systems within a building.
Anyone have a copy of the 2004/5 CEC to know if this got changed to the 2002 wording? Are we still bonding gas to the GEC?