Posted By: BigJohn GFCI Near Laundry Sink? - 09/06/05 10:29 PM
Recently red-tagged on a new-house construction because there was no GFCI protection for a receptacle on the wall opposite of a laundry-room sink. Inspector said all receptacles within 6' of the sink in any direction must have ground fault protection.

Not saying it isn't a good idea, but I couldn't find the article requiring it. 2002 NEC. Anyone have a reference?

-John
Posted By: Roger Re: GFCI Near Laundry Sink? - 09/06/05 10:48 PM
BigJohn, it is a new wording in 210.8(A)(7) of the 05 NEC.


Quote
Laundry, utility, and wet bar sinks — where the receptacles are installed within 1.8 m (6 ft) of the outside edge of the sink

If you are still under 02 the inspector is wrong.

Roger
Posted By: HotLine1 Re: GFCI Near Laundry Sink? - 09/06/05 10:49 PM
210.8 (a) (7) of 2005 NEC

John
Posted By: Roger Re: GFCI Near Laundry Sink? - 09/06/05 10:52 PM
I snuck that one in on you John. [Linked Image]

Roger
Posted By: BigJohn Re: GFCI Near Laundry Sink? - 09/06/05 10:56 PM
I knew it. And I had to drive thirty miles to correct that bogus violation. [Linked Image]

Thanks, gentlemen.

-John
Posted By: HotLine1 Re: GFCI Near Laundry Sink? - 09/07/05 10:26 PM
Roger:
OK, you type faster than me. I was going back to edit, but ya got me.

John