Posted By: watersparkfalls pipe fill - 07/18/05 06:11 PM
will a 6-3 romex fit in a 3/4" pvc?
not sure how to calculate the 53% single conductor.

thanx,
h2o
Posted By: George Re: pipe fill - 07/18/05 08:19 PM
I believe for Southern Wire Corp the diameter is .683".
Posted By: winnie Re: pipe fill - 07/18/05 08:47 PM
Take the largest diameter across the cable. Calculate the cross section area is if the cable were round with this diameter. (PI*D^2)/4

Divide this by the internal area of the conduit. If the answer is less than 0.53, you are good to go.

-Jon
Posted By: Electric Ian Re: pipe fill - 07/19/05 12:09 AM
Looks like you need to go to 1"

assuming .683 diameter:

Area = Pi*r^2 = 3.14*.3415^2 = .366
assuming sched 40 PVC:
max allowable 53% fill area for 3/4" is .269 (too small)
max allowable 53% fill area for 1" is
.441 (that'll work)
Posted By: watersparkfalls Re: pipe fill - 07/19/05 06:04 AM
thanx guys....

h2o