a friend asked me if a 125 amp sub panel would be ok for three water heaters that are 40 amps each.
Posted By: Larry Fine Re: h20 heaters - 07/17/05 03:51 PM
Is the 40 amps the actual heater current, or the individual circuit ratings?
Posted By: watersparkfalls Re: h20 heaters - 07/17/05 03:56 PM
individual circuit ratings
Posted By: renosteinke Re: h20 heaters - 07/17/05 04:30 PM
Really comes down to the application.

If you're talking about water heaters used as household ones are....heating separate systems, and used occasionally for brief periods, the 125 amp panel should be fine.

If these are used together, as in supplying hot water to a production process, and use continuously, than you have to treat the loads as continuous, and have that 25% "buffer' added in to both your panel and the wire supplying it.
(Use the KW ratings of the heaters for your calcs).
Posted By: Larry Fine Re: h20 heaters - 07/17/05 10:24 PM
At max proper circuit loading, which would be (40a. x 80%) 32a. each, that's 96 a. total.

Another way, 3 x 40a. = 120a. Either way, you're okay.