Posted By: gunner Dual channel service - 06/03/07 11:18 PM
I'm replacing 60 a. with 100 a.panels in a two family home is it permitted to use a 2/0
service cable rated at 150 a.to feed the meter channel or do I have to use a 4/0 200 a. cable.
Posted By: gfretwell Re: Dual channel service - 06/04/07 01:01 AM
I see this as a 200a service, 2/0 cu or 4/0 al. The multifamily break in 220.32 starts at 3 units