ECN Forum
Posted By: Trumpy Lock-Out Mechanisms? - 06/30/03 06:13 AM
Where you work,
How do you make sure that the Circuit-Breaker, that you have just isolated or the HRC fuse is not replaced on you?.
With using HRC fuses, there is no real way (I feel), apart from taking the fuse carrier AND the fuselink with you, if you are working at a site, remote from the supplying panel.
How would you normally lock-out a proprietary Circuit Breaker?.
Any thoughts on this subject, would be greatly encouraged.
Posted By: pauluk Re: Lock-Out Mechanisms? - 06/30/03 10:02 AM
This isn't usually a problem in the sort of small-ish premises in which I work, but if I feel that there might be a risk of someone re-closing a breaker I'll take a few minutes to remove the panel cover and physically disconnect the wire.
Posted By: sparky806 Re: Lock-Out Mechanisms? - 06/30/03 11:43 AM
It's simple. Each of my guys has been issued a lock out/tag out kit, and is required to use it. He/She is the only person allowed to have a key to their lock. If locking out is impossible, then remove wires from sorce, but still required to "tag out" the equipment.

I was working on some 480 volt hi-bays a few years ago, and caught an employee of the customers trying to break my lock off of the panel to turn the lights back on. After he was arrested for criminal damage to property, he was sent to the unemployment line.
Richard
Posted By: pauluk Re: Lock-Out Mechanisms? - 06/30/03 10:44 PM
Sheesh.... Some people! [Linked Image]

I wonder whether he thought somebody had put the lock there just for the fun of it?
Posted By: PCBelarge Re: Lock-Out Mechanisms? - 07/01/03 10:09 AM
Sparky806

The frightening part of your story is it is not only enough for us to be trained in lockout/tagout, but what about the untrained trying to remove the lock? I was an apprentice working with a mechanic, and we were working on 277v lighting. we had turned off the breaker, but not locked or tagged. We were in the building alone ( new building, punchlist). All of a sudden he started bouncing around the 2x2 ceiling grid like a top (the building super saw the breaker off, and turned it back on). At first I thought he was fooling around, finally I had to pull the ladder from under him. He broke his leg and sustained multiple burns. I have been a safety nut ever since.

Pierre
Posted By: Trumpy Re: Lock-Out Mechanisms? - 07/12/03 05:48 AM
Here's a picture of a typical Lock-Out tag,
that we use over here.

[Linked Image]

It's made out of a special type of paper that has plastic mixed with it, so it won't tear!.(I've tried it.)
Posted By: pauluk Re: Lock-Out Mechanisms? - 07/12/03 10:10 AM
Interesting tag for New Zealand. It looks much more like an American tag than anything used in Britain.
Posted By: Scotts Re: Lock-Out Mechanisms? - 07/13/03 05:14 PM
OSHA also mandates that the tag has to be attached with a non reusable "thing?" that is capable of withistanding 50 pounds of force. Sorry for the thing word, having a brain fart right now. The reson is do that it is harder for an unathorized person to take off the tag. Basically they mean a 1/4" wire tie. If the tag is put on with some string, or wire, it is easy for somone to undo the knot and remove the tag.

I received a catalog from a sign company that was selling the tags you pictured. However they had wire in the eye for people to use when attaching the tag. I e-mailed them about it and said they were selling something that is non-compliant. In their return e-mail they blew me off.