Posted By: alanh Ground Fault Circuitry - 02/28/02 07:37 PM
I work in a law-firm (not a lawyer though, thank God). We have a case where a freezer leaked some water that got into the electrical outlet, started a fire and caused the house to burn down.
An expert has inspected the scene and came to two conclusions regarding liability.
1. The freezer should have been connected to a "Ground Fault Circuitry" .
2. The builder should not have used 16 penny nails connecting the outlet box to the stud. Once the outlet box got hot, the nails then overheated causing the wood to burn around them.

I have my own opinions regarding this person's conclusions, but I would appreciate the thoughts of some of the non-biased experts here.
Thanks a lot.
Alan Heaberlin
Posted By: motor-T Re: Ground Fault Circuitry - 02/28/02 08:15 PM
alanh;
First what you described seems to be correct. the Freezer is a dedicated circuit with a single attachment receptacle does not have to be gfci protected. And unless it was a ground-fault the gfci would not have tripped anyway. To genrate that kind of heat there had to be one Heck of a short inside that box to where the nails got so hot to cause the fire
You didnt state if the box was plastic or metal but they both can be nailed to a stud with nails.
Did anyone even bother checking why the breaker didnt trip ? Or if the freezer was malfunctioning ? And what Non-metal fastener is recommended to hold boxes to studs ?
I dont have my code book in front of me right now but someone will quote you chapter and verse.
it just burns me up that the contractor takes all the heat. Once this stuff is installed who knows what evil lurks in the average homeowner as far as revising what was done during construction.
-Mark
Posted By: Bill Addiss Re: Ground Fault Circuitry - 02/28/02 09:55 PM
Alan,

Can you supply more details?

Where was the Freezer (room) and is it the Freezer outlet that is theorized as starting the fire? Where was the outlet? Height, etc.
How did water get in there and how much are we talking about? Copper or Aluminum wiring? Original 'builders' outlet or was it replaced by someone etc.

Bill
Posted By: resqcapt19 Re: Ground Fault Circuitry - 02/28/02 09:59 PM
Who paid the "expert". Many times their conclusions are based on who is footing the bill.
The use of nails to support the box is a standard practice. Some boxes come from the manufacturer with pre-installed nails that are crimped inside the box so that they can't fall out before the box is installed. Where was the freezer installed? Most of the time GFCI protection would not be required.
Don(resqcapt19)
Posted By: Electricmanscott Re: Ground Fault Circuitry - 02/28/02 10:49 PM
The "experts" conclusions show he is not an expert after all. Without more info it soundslike aperfectly code compliant installation. I would also be more interedsted to find out why the breaker did not trip. I can not even begin to believe that some water leaking from a freezer could cause a short that would sustain itself long enough to heat nails to the point that the wood would ignite. This is very interesting.
Posted By: George Corron Re: Ground Fault Circuitry - 02/28/02 11:07 PM
In summation, your experts conclusions are based on neither National Electrical Code, nor conventional trade practice. [Linked Image]
Posted By: CTwireman Re: Ground Fault Circuitry - 02/28/02 11:50 PM
Should not have used nails? What should he have used? Glue? To place blame on the builder for using a common nail-on box is outrageous and ridiculous.

I cant see how nails contributed to the fire. (as eveyone above has correctly pointed out)

GFIs arent designed to prevent fires, they are designed to prevent shock.

What field was this person an "expert" in?



[This message has been edited by CTwireman (edited 02-28-2002).]
Posted By: Nick Re: Ground Fault Circuitry - 03/01/02 12:33 AM
I have to concur with the above posts. Nailing boxes to wood studs is a standard trade practice. If it is dangerous then 99.9% of the homes in America are in big trouble. No codes violated here.
Posted By: rbiro Re: Ground Fault Circuitry - 03/02/02 01:12 AM
Something seems fishy to me.

I would try to find out preciesly what the "expert" really said. He may have said that current code requires the outlet in question to be a GFCI outlet (assuming it's for a kitchen counter and not for the freezer) and may have said that the nail transmitted the heat from the box to the wood, which could be true. Someone else could than have transformed his statements to blaim the builder/electrician. Then again, the "expert" could just be full of sh*t.
Posted By: circuit man Re: Ground Fault Circuitry - 03/02/02 03:27 PM
i'm not an expert, but as the rest of the guys said boxes have been nailed to studs forever. as for as them transmitting heat like that, the breaker should have tripped lon before this ever happened. it wasn't a FPE type breaker by chance? these are notorious for not tripping as i found out in 1980 while i was at tech. big class action lawsuit against them. but guess what, that didn't stop them. another company took over & started making them again. as for the gf it is as the guys said for shock protection not overloads.sounds like the guy saying this is working for the insurance adjuster , not the home owner. hope you keep us posted.
Posted By: resqcapt19 Re: Ground Fault Circuitry - 03/02/02 04:19 PM
This was most likely an arcing fault and would never pull enough current to open a breaker. The fire may have been prevented by an AFCI depending on the type of arcing that produced the heat. It sounds like a poor quaility connection on the receptacle that was producing heat when there was a load. If so this wa a series arcing fault and even an AFCI might not detect this fault. If it was an arc between the hot and grounded conductor, that would be a parallel arc, and an AFCI would have opened the circuit.
Posted By: Bob Re: Ground Fault Circuitry - 03/02/02 07:27 PM
I do expert testimony and this guy sounds like a nut. There is no requirement fo put a freezer on a GFI. You would not want to do this for fear of a power outage and the freeezer defrosting. From what you have posted there must be a lot more to this that what you have said. I would like to know how it was determined that the water leaked into the outlet. Check out the freezer itself. It may be defective and caused an overload.
Also check out why the breaker did not trip.
You did not say whether the outlet box was metal or plastic. It would be more likely that an arc may have started the fire. Anyway I think your expert is nuts.

[This message has been edited by Bob (edited 03-02-2002).]
Posted By: ggardiner Re: Ground Fault Circuitry - 03/03/02 07:13 PM
I have a question about the inspector was he an electrical expert or an expert at getting insurance companies off the hook. If what he said is right then many houses in North America are in serious trouble. I would be interested in his recommendation on how to install a box though that really could be interesting and I'd like to see him install it.
Posted By: electure Re: Ground Fault Circuitry - 03/03/02 07:43 PM
Don, I thought you disliked AFCIs?
Posted By: resqcapt19 Re: Ground Fault Circuitry - 03/04/02 03:02 AM
electure,
I don't like them because they have been represented as a "cure all" for electrical fires. Notice that I stated that they may have prevented this fire if the cause was a parallel arcing fault. A GFCI breaker will also detect and clear all parallel arcing faults on any wiring system that is compliant with all editions of the NEC that require the use of an EGC in the raceway or cable. I have stated that I do believe that they will act to provide protection from parallel arcing faults, but I believe that the vast majority of electrical faults are of the series type.
Don(resqcapt19)
Posted By: HIGHVOLTAGE Re: Ground Fault Circuitry - 03/04/02 03:35 AM
A GFCI would not have prevented this fire
I have witnessed this happen , it at best will trip the GFCI outlet , but remeber the power is still there ,
this GFCI got wet and it melted , it's a good thing someone was there or there would have been a bad thing .
They should get an investigator who has knowledge of this kind of thing
Posted By: alanh Re: Ground Fault Circuitry - 03/04/02 01:34 PM
Wow. I never expected this. It was a metal outlet box in a manufactured home. The expert said that smaller nails should have been used to attach the box to the stud, not the 16P. We have determined already that the freezer was faulty in that it had a leak and the water somehow allegedly leaked into the outlet causing the fire. I don't know if the outlet was dedicated for the freezer. That's actually a great question. Thanks for all of your replies, they are very helpful and I'll keep you all updated on the outcome.
Alan
Posted By: resqcapt19 Re: Ground Fault Circuitry - 03/04/02 04:36 PM
Highvoltage,
I said a GFCI breaker would open the circuit on a parallel arcing fault in a code compliant building wiring system. It is very nearly impossible to have a parallel arcing fault on a building wiring system that is not also a ground fault.
Don(resqcapt19)
Posted By: Scott35 Re: Ground Fault Circuitry - 03/04/02 06:39 PM
Alan,

Unfortunately, you have been involved with an "Expert Of Bull****" [A Quack Of All Trades], in regards to this Freezer situation.

First off, as everyone has prevoiusly mentioned, GFCI protection is used to protect personnel [AKA The person(s) using an Appliance] in the event of a shock hazard posed to them from a Ground Fault situation [shock to Ground].

The only way a GFCI would be effective in the situation you are describing is if the Water leakage from the Freezer caused a high enough Ground fault current to "Leak" on the "Load" side of the GFCI device.
That may have tripped the GFCI and prevented the resulting fire.

That is only an assumption, and it leaves too many areas wide open, in which the resulting fire may have started much easier and the GFCI would not have been able to trip - even if the device was operating better than "average".

2: If the Investigating Person told me that a Metallic Outlet Box with smaller than 16d nails used for support of the Box, would have any merit in nullifying the heat transfer during a fire, I would ask the person to take a Breathalizer Test first to determine the Person's Toxicity / Blood-Alcohol level, then do a Psych. evaluation test to determine the Person's state of mind [only after verifying that the date is not 04/01/xx]
[Linked Image]

In all seriousness, the fact that the person has passed their own opinion of very questionable merit to ANYONE INVOLVED with the event sounds like a free ticket to dismissal from future investigating tasks!
[AKA Pink Paycheck w/ the word "Termination" printed on it!]

Here we have a Metallic Outlet Box, supported by 16d nails, in an enclosed wall made of combustible materials.
The Framing Members ["Studs"] will also have 16d nails driven through them; at the Top Plate, Bottom Plate, and to secure "Fire Blocks".
Many Metallic "Ties" used in Framing are also secured with 16d nails.

If the Metallic Outlet Box was the primary source for heat sinking [Conducting the heat from the fire to a cooler spot/spots], wouldn't this be more prone to set fire to the stud? [personally, I think the heat will concentrate on the box, then conduct much easier to the surrounding air way before flames begin to appear on the stud].
Also, if the nails are thin as compared to the heat sink, and they extend into a material which does not heat sink as easilly as the metallic items will, won't this RETARD THE HEAT TRANSFER [nullify it's conduction]???

Time to ask this Investigator to go back to his/her planet of origin and do Investigations there.
If returning to Earth, prior to doing Investigations again, be sure this person becomes more educated on the simple laws of Physics for this planet [Linked Image]

Sounds like a Quack to me!

I can see the OCPD not tripping in this event, as the load current probably did not exceed 10 amperes [lucky to see that level].
This would be a really loud and scarry fault, but of very low magnitude.

This type of event would be a prime target for AFCI devices [as pointed out by others]. GFCI's and standard OCPD's would offer very little, if no protection in this situation.


[disclamer]Just My $0.02! Not verified proof, or relavent data[/disclamer]

Scott SET
Posted By: nesparky Re: Ground Fault Circuitry - 03/04/02 11:17 PM
Suggest you look in the phone book under electrical contractors, pick out two or three of them and have each look at the property. Ask them thier opinions in writing. They will be a lot more realistic than the paid b***s****er you currently have.