Posted By: wendel Extension Cords-Which to Use First? - 12/06/06 07:57 PM
I have two extension cords both are 50 feet long. One is 12 gauge and the other is 14 gauge. I want to power an electric saw.

I want the least voltage drop over the combined 100 feet so I keep the current draw by the saw motor as low as possible minimizing heat damage. Which should I plug into the 120 volt receptical first? Why?
Posted By: scameron81 Re: Extension Cords-Which to Use First? - 12/06/06 08:16 PM
I don't think it matters. The resistance will be the sum of the two extension cords regardless of which one comes first and the distance is still the same. But I could be wrong (it wouldn't be the first time.)
Posted By: SvenNYC Re: Extension Cords-Which to Use First? - 12/06/06 08:53 PM
Yeah....it's still, essentially two resistors in series. Don't think it really matters which "gets it" first.

If it makes you feel better, though, I'd go with the #12 first and then hook in the #14.

Of course I betcha the wiring in the wall is #14.... [Linked Image]

Would there really be THAT much voltage drop over that much wire?
Posted By: pauluk Re: Extension Cords-Which to Use First? - 12/06/06 09:15 PM
It's all going to be one series circuit whichever way you do it:

#1. Hot -> 50' #12 -> 50' #14 -> Tool -> 50' #14 -> 50' #12 -> Neutral.

#2. Hot -> 50' #14 -> 50' #12 -> Tool -> 50' #12 -> 50' #14 -> Neutral.

Either way you have 100 ft. of #14 plus 100 ft. of #12 conductor in the circuit, so the resistance of the extension cords will be the same.
Posted By: rabbitgun Re: Extension Cords-Which to Use First? - 12/06/06 09:36 PM
Nope it does not matter.
That said, even with a 16A load the drop is only right around 4 volts.
Posted By: e57 Re: Extension Cords-Which to Use First? - 12/07/06 08:15 AM
Have you thought of installing an outlet closer? [Linked Image]
Posted By: Zapped Re: Extension Cords-Which to Use First? - 12/07/06 02:34 PM
Two resistors in series: R(total)=R1+R2. No difference with placement. If it's causing you to lose sleep, spend the $20 on another 50' #12 extension.
Think about inrush current, though. Get a 100' 10/3 cord. just a thought.