Posted By: doninphx load calculations - 10/05/06 08:51 PM
I was woundering if any one had a quick way to calculate a sub panel load. 3 ph 208.
Posted By: ShockMe77 Re: load calculations - 10/05/06 10:05 PM
What are the loads going to be?

Air conditioning, welders, lighting, etc....
Posted By: doninphx Re: load calculations - 10/06/06 11:37 AM
the loads are small conveyors, fractional HP motors 120 v single phase and a computer with a 60 watt light at each station.
Posted By: Almost Fried Re: load calculations - 10/06/06 06:26 PM
Don in Phoenix:
There ain't any easy way, ya gotta do the math. Get a pencil out, list every load, in that application I would assume 100% duty cycle. Ask the customer what he plans on ading over the next couple of years, total it up, add 25% and then round up to the next larger size panelboard. Convenience outlets with no load are calculated at 180 vA. Or you can just fake it with a 225 A MLO 42 circuit, NQOD bolt on box, fed with copper enough to overcome the distance, then they will say nice things about you long after you're gone...