Posted By: steve ancient apprentice Bonding of pool pump - 06/28/06 01:01 AM
We installed wireing for a pool the other week. Everything passed but how exactley is a non-double insulated pool pump motor bonded. I know its a # 8 Bare but what is the exact procedure. The more I read the code book the more confused I get. Any and all help would be greatley appreciated. If you dont have enough room in this forum please e-mail me at anna729@comcast.net I live in massachuttes. Wish school was still open. My boss isnt even sure of the answer. HELP
Posted By: HotLine1 Re: Bonding of pool pump - 06/28/06 01:09 AM
Steve:
Short & sweet, lug on motor to pool frame.
IF any other pool equipment, continue #8 accordingly. Anything within zone over 4Sq in. has to be bonded.

IG pool is rebar, niche shell, cups, filter, heater etc.

Basically, if in doubt, bond it.

Do not go to a grd rod, panel, sub-panel, EGC etc.

NOTE: Be very careful if it's inground in areas that adopted 2005 regarding bonding around perimeter decking. I don't have Article handy now, but read!

John
Posted By: Peter Salegna Re: Bonding of pool pump - 06/28/06 01:21 AM
If above ground every stantion must be bonded, holes in stantions must be drilled and taped and the lug must be suitable for direct burial. the #8 min must be connected @ every stantion then go to the pump motor with no break.
Posted By: gfretwell Re: Bonding of pool pump - 06/28/06 03:12 AM
Peter, is that a metal pool with significant metal to metal contact between members? If so I say it goes beyond 680.26
With that thinking we would be looping our screen cages with #8.