Posted By: Fred Over-voltage - 06/12/06 01:36 AM
Had a neighbor call Friday afternoon. She said her power supply on her PC went bad and she called her computer guy out. He replaced the power supply and plugged the computer in and in 2 minutes it was smoked too. He replaced the power supply 2 more times with the same result before she called me. I checked voltage at her surge strip, which had a red indicator light showing "surge", and I was showing 142 volts. My first thought was open neutral so I proceed to the panel and find 142V on each line to ground and 284V between lines. We live out in the boonies about a mile apart. I call the line super at REMC and tell him what I have. He says that makes 4 in our township this week and sends a couple of guys out with a new tranny. We have had several thunder boomers last week so it must have been lightning. The tranny was only 10 years old and didn't show any outward signs of damage. I told the computer guy the next time he has a customer call with a power supply fried, check voltage before he replaces it and plugs it in. He could buy a good Fluke volt meter for what a power supply costs, or at least for what he charges for one.
Posted By: Elviscat Re: Over-voltage - 06/12/06 01:45 AM
he replaced the power supply three times? after the first two go up in smoke in only a few minutes isn't that the sign to stop trying?
Posted By: hypress Re: Over-voltage - 06/12/06 02:27 AM
What it sounds like to me is a turn to turn short in the primary of the pole transformers. Lightning storms will cause that.
Posted By: BigB Re: Over-voltage - 06/12/06 03:34 AM
Reminds me of a call I had where the service neutral had opened. Fried the big screen tv, the guy brought in the bedroom tv, fried it too, then he hooked up a 3rd tv, you guessed it, fried that one too.
Posted By: Radar Re: Over-voltage - 06/12/06 04:26 PM
142V is a little tough on light bulbs too.

Isn't it a little strange that the problem shows up equally on both sides of the transformer's center point?
Posted By: Texas_Ranger Re: Over-voltage - 06/12/06 05:06 PM
Hmmm... problem on the HV side? _that_ would definitely cause a higher but balanced voltage!
Posted By: wa2ise Re: Over-voltage - 06/12/06 07:50 PM
As far as overvoltage from the POCO goes, about 15 years ago the entire town here had about 132/264V on one of the 3 phases. Took the POCO about a month to straighten it out. Seems the loads on the 3 phases was out of balance over the entire town.

Another time, when the big blackout in the Northeast in August a few years ago, I didn't lose power, but the line voltage oscillated from 90V to 140V every half minute for about an hour. I turned off all the air conditioners, fridge, freezer and the dehumidifier when that happened. The PC didn't mind it for several minutes and then I unplugged it as I didn't want to push my luck...
Posted By: WFO Re: Over-voltage - 06/13/06 03:00 AM
Since I work for a POCO, I feel like a little bit of a traitor, but if that happened on our system, we, as the POCO, would be liable for damages.
I suggest your friend look into this.
Posted By: RODALCO Re: Over-voltage - 06/13/06 07:42 PM
It look that it could be a tapchanger problem in the local substation.

If the AVR or tapchanger developed a fault the tapchanger keeps stepping up and may cause a high voltage on the 11 or 13.2 kV primary side of all transformers connected to a particular sub.

hence all the low voltages (115,230) will be on the high side.

How many taps does the primary side of US substation transformers have ?

In New Zealand there are 17 steps . from where tap 5 is the 33 kV point.