Posted By: Happi_Man Smoke/CO2 Detector Combo Units - 03/03/06 05:31 PM
Anyone have any great knowledge of these god forsaken things?

It seems like every other job I get a "bad" one. We wire our smokes on their own 15 AMP circuit and interconnect them using 14/3 romex. They go on an arc fault breaker. We then use a combo unit in the basement if there are gas mechanicals. Anyone see any problem with that. The combo units are the same manufacturer as the smokes. Typically what we are getting is that when you push the test button at the combo its sets off all the units except itself. Its driving me batty!

Are these things simply that unreliable or are we doing something wrong?

Any thoughts?
Posted By: mshaw Re: Smoke/CO2 Detector Combo Units - 03/03/06 07:57 PM
Are they UL listed to be used togather with the other units?
Posted By: Celtic Re: Smoke/CO2 Detector Combo Units - 03/03/06 09:10 PM
What brand and model # smoke/co units?
Posted By: Joey D Re: Smoke/CO2 Detector Combo Units - 03/04/06 12:47 AM
FireX? I have had the same thing happen and now use BRK and will do so until I have issues with them.
Posted By: Happi_Man Re: Smoke/CO2 Detector Combo Units - 03/04/06 10:56 PM
That's what I was lookin' for...yep, they are Firex. I was using BRK but they're so damned expensive. I guess therein lies the phrase "you get what you pay for".
Posted By: Speedy Petey Re: Smoke/CO2 Detector Combo Units - 03/05/06 02:48 PM
There was a long run with the Firex CO/smokes having problems. I'd get a bad one every fourth or fifth one.
They have improved them and changed the p/n to 12000 from whatever it was and I have seen MUCH less issues with them.
Posted By: Happi_Man Re: Smoke/CO2 Detector Combo Units - 03/09/06 06:47 PM
Found out from Firex that some of the issues are actually misunderstandings. If you push the test buttom of a smoke detector or a smoke/co2 it will set off all of the alarms in the house except for itself. So its not actually "bad", its just working the way they've designed it to. I guess then to be sure you have to go to each alarm and push the test button. Probably should do that anyhow, right?
Posted By: derater Re: Smoke/CO2 Detector Combo Units - 03/19/06 10:49 PM
Combo smoke/CO devices are a bad idea to begin with; smoke rises CO/CO2 is heavier than air so it sinks. I'd never use them.
Posted By: daffy03221 Re: Smoke/CO2 Detector Combo Units - 03/20/06 01:16 AM
Derater is right, combo units suck, they are more costly than individual smoke and CO2, and the CO2 detector should be down by the furnace or whatever the heat is in the house, halfway down the wall. Have to ask, how does the 14-3 work on an arc fault? Won't that trip the breaker?
Posted By: mxslick Re: Smoke/CO2 Detector Combo Units - 03/20/06 03:04 AM
daffy03221:

Welcome to ECN!

In this case, the 14/3 is most likely wired as Black = hot, white = neutral RED = "signal" (or "interconnect") which is a low-voltage link between units.

So this would not be the dreaded multi-wire application. [Linked Image] Thus no issue at all with the even more dreaded arc-faults.
Posted By: Electricmanscott Re: Smoke/CO2 Detector Combo Units - 03/20/06 11:40 AM
Quote
Combo smoke/CO devices are a bad idea to begin with; smoke rises CO/CO2 is heavier than air so it sinks. I'd never use them

This is misinformation. Co detectors can be mounted on walls, or ceilings, up high or down low. It does not matter because carbon monoxide is only slightly more dense than air it mixes in with the air quite well so location of the detector does not matter.
Posted By: Active 1 Re: Smoke/CO2 Detector Combo Units - 03/20/06 01:37 PM
What I wonder about the combo units is if it creates confusion if it's a fire of CO leak. I know they have some now that talk while I think the others had lights.

We did them interconected with the somkes as combo units and seperate units with their own switch leg only to CO. I like the 2nd way better. Seems like the more you interconect the harder it is to find the bad one.

Most places here don't have CO requirements so it's a upsell or just on the print.

Tom