Posted By: NJI grounding fields? theory - 11/05/05 06:03 AM
can anyone explain the hazards of running a 4wire subfeed 120/240 AND puting in ground rods. Other than the fact that you shouldn't i'd like to brush up on the theory behind it.
Posted By: resqcapt19 Re: grounding fields? theory - 11/05/05 01:09 PM
NJI,
Quote
can anyone explain the hazards of running a 4wire subfeed 120/240 AND puting in ground rods. Other than the fact that you shouldn't i'd like to brush up on the theory behind it.
Who told you that you shouldn't do both? If the sub panel is at a second building and you pull an EGC, the code requires a grounding electrode system at the second building.
Don
Posted By: NJI Re: grounding fields? theory - 11/06/05 03:45 AM
As I have understude my AHJ one or the other. Can you give me my code references? I thought one or the other. four wire or three and a rod.
Posted By: Larry Fine Re: grounding fields? theory - 11/06/05 03:47 AM
No, it's bond neutral to ground, or 4-wire.
Posted By: Roger Re: grounding fields? theory - 11/06/05 03:53 AM
NJI, read 250.32

Roger
Posted By: NJI Re: grounding fields? theory - 11/06/05 04:14 AM
thanks, i'v been searchhing past posts and am reading as we speak..workin on it