Posted By: zxone lra? - 11/04/05 11:52 AM
what should an amp draw be at start up
on a a/c compressor?

zxone
Posted By: Roger Re: lra? - 11/04/05 12:07 PM
That would depend on the size of the compressor.

Roger
Posted By: Wolfgang Re: lra? - 11/04/05 01:59 PM
nominal amps time 6 is minimum for start.
Posted By: Redsy Re: lra? - 11/04/05 11:14 PM
A motors code letter indicates how much kVA per HP with a locked rotor.
See Table 430.7(B).
Posted By: zxone Re: lra? - 11/05/05 12:12 PM
thank you for the infomation

zxone