Posted By: bot540 Neutral Current Carrrying? - 09/16/05 01:52 AM
I know this has probally been asked a thousand times but does the neutral in a 2 wire single phase circuit(ie: a small apliance branch circuit) count as a current carrying conductor?
Posted By: iwire Re: Neutral Current Carrrying? - 09/16/05 01:59 AM
You don't have a neutral in a two wire circuit. [Linked Image]

You have a ungrounded conductor, a grounded conductor and maybe a grounding conductor.

Both the ungrounded conductor and grounded conductor are current carrying conductors.

Bob
Posted By: Roger Re: Neutral Current Carrrying? - 09/16/05 02:02 AM
Absolutely, in a 2 wire circuit it is impossible to have a neutral conductor. Click Here

Roger
Posted By: Roger Re: Neutral Current Carrrying? - 09/16/05 02:05 AM
I was a little slow on that one Bob. [Linked Image]

Roger
Posted By: bot540 Re: Neutral Current Carrrying? - 09/16/05 02:13 AM
Thanks guys I just read the post in the nec forum and understand.
Posted By: Attic Rat Re: Neutral Current Carrrying? - 09/16/05 02:13 AM
...Bob,I may be wrong here,but,isn't the grounded conductor considered current-carrying ONLY when used in circuits where there are non-linear loads harmonics,such as HID lighting,servo controls,ballasts,or in a 3 phase wye utilizing only 2 phases and a neutral...etc??otherwise,if the circuit is balanced,the current on the neutral is 0,you wouldn't count it as current -carrying for derating purposes,ampacity..??
Russ
Posted By: winnie Re: Neutral Current Carrrying? - 09/16/05 02:19 AM
Attic Rat, the OP was asking about a two wire circuit, not a multiwire circuit where current could balance in the neutral.

-Jon
Posted By: Attic Rat Re: Neutral Current Carrrying? - 09/16/05 02:21 AM
Ooops,..my bad... [Linked Image] [Linked Image]
Posted By: bot540 Re: Neutral Current Carrrying? - 09/16/05 02:37 AM
Does a grounded conductor have to be perfectly balanced in order not to be counted as a current carrying conductor? Can someone give a feild example?
Posted By: Attic Rat Re: Neutral Current Carrrying? - 09/16/05 02:42 AM
... Take a normal 3 phase wye circuit,..all sharing the neutral,and the loads close to being equal...(barring the use of HID fixtures,processors,variable speed drives etc)and you should have a balanced circuit..
Russ
Posted By: iwire Re: Neutral Current Carrrying? - 09/16/05 02:42 AM
Bot whatever we call it, the ungrounded, the white wire or if you want neutral is always a current carrying condutor in a two wire circuit.

If the current does not flow on the neutral the circuit is off or has a ground fault.

The only time neutrals are sometimes not current carrying conductors are when they are a part of a multiwire circuit.

Which is a circuit that consists of two or more ungrounded conductors that have a voltage between them, and a grounded conductor that has equal voltage between it and each ungrounded conductor of the circuit and that is connected to the neutral or grounded conductor of the system.
Posted By: bot540 Re: Neutral Current Carrrying? - 09/16/05 02:52 AM
iwire the question was in reference to a multiwire circuit. I understand the theory behind a grounded conductor becoming a "neutral". The reason I asked for a field example was because it seems rare to have a true neutral. I know that the loads on cancel each other out but how often do you see the loads on each ungrounded circuit exactly the same? I was just thinking that this is barely ever used in determining conductor size or am I wrong?
Posted By: iwire Re: Neutral Current Carrrying? - 09/16/05 03:08 AM
I got you now bot and you can call me Bob.

I run as many multiwire branch circuits as I can.

It is fairly unusually for the neutral not to actually carry some current.

It is much more likely that each phase will be carrying different currents and the neutral will be carrying the amount of imbalance.

This does not change the fact that for derating purposes many times the neutral in a multiwire circuit that carries current is still not counted as a current carrying conductor.
Posted By: winnie Re: Neutral Current Carrrying? - 09/16/05 03:22 AM
bot,

There are two different meaning for the term 'current carrying conductor'. One is to ask the question: Is there current flowing in that conductor? The second is to ask the question: Given a particular arrangement of conductors in a conduit, how much must I derate the current handling capacity of the conductors?

The answer to the _second_ question is not based upon the actual current flow in the wires, but instead on the current flow in the wires during the 'worst case' possible condition.

In the case of a single phase three wire circuit, the worst case condition is two wires carrying full current and the other wire carrying nothing. Call the two hot wires HotA and HotB; then you might get 20A on HotA and 20A on HotB, or 20A on HotA and 20A on the neutral, or 20A on HotB and 20A on the neutral. These are the worst case scenario for heating, and in this state there are only two wires carrying current. So for the purpose of derating, this set of conductors _counts_ as two 'current carrying conductors'.

Now what happens to all of the other possible states? You could have, for example 20A on HotA, 10A on HotB, and 10A on the neutral. Clearly all _three_ conductors actually have current flowing in them...but if you do the calculations you will find less heat produced than in any of the 20A and 20A conditions. So by treating this set of three conductors as only two 'current carrying conductors', you end up with a conservative estimate of heat production.

Similarly, in three phase service, with three hots and one neutral, the worst case is _three_ current carrying conductors, except for the case of harmonic current flows, where you can see all _four_ conductors carrying heavy current.

-Jon
Posted By: techie Re: Neutral Current Carrrying? - 09/16/05 12:16 PM
There is actually an even worse case scenario.
When feeding 3 phase dimmer racks, such as in a theatre, where the loads on each phase vary, under certain conditions, the load on the neutral can exceed the load on any individual phase.
If you look in the NEC under section 520, you will find a requirement that feeders for dimmer racks be provided with a neutral twice the size of the phase conductors.
Posted By: iwire Re: Neutral Current Carrrying? - 09/16/05 12:26 PM
Techie actually those dimmer racks are non-linear loads that cause the harmonic currents on the neutral that Jon mentioned.

Audio amps have the same issue.

This fall I will be installing two additional 400 amp three phase 4 wire disconnects on a 'shed' stage for lighting, video or sound.

I am trying to get the customer to go with K rated transformers and double neutrals.

Bob
Posted By: iwire Re: Neutral Current Carrrying? - 09/16/05 12:39 PM
Techie I can not find anything in 520 that requires that feeders for dimmer racks be provided with a neutral twice the size of the phase conductors.

What I do find is requirements to treat the neutral as a current carrying conductor.

I think there is a move among the better traveling shows to want double neutrals from the venue disconnect to their distribution equipment.
Posted By: techie Re: Neutral Current Carrrying? - 09/16/05 10:22 PM
Quote
Techie I can not find anything in 520 that requires that feeders for dimmer racks be provided with a neutral twice the size of the phase conductors.

I don't have a copy of the code handy, but google and mikeholt indicated that it might be 520.53(o). I think it was added in 1993.
Posted By: gfretwell Re: Neutral Current Carrrying? - 09/17/05 01:39 AM
(O) Neutral.
(1) Neutral Terminal. In portable switchboard equipment designed for use with 3-phase, 4-wire with ground supply, the supply neutral terminal, its associated busbar, or equivalent wiring, or both, shall have an ampacity equal to at least twice the ampacity of the largest ungrounded supply terminal.
Posted By: iwire Re: Neutral Current Carrrying? - 09/17/05 10:28 AM
Greg, Techie, 520.53(O)(1) only applies to the internal construction of the portable switchboard equipment. 520.53(O)(2) is more interesting.

IV. Portable Switchboards on Stage
Quote
520.53 Construction and Feeders.
Portable switchboards and feeders for use on stages shall comply with 520.53(A) through (P).

(O) Neutral.
(1) Neutral Terminal.
In portable switchboard equipment designed for use with 3-phase, 4-wire with ground supply, the supply neutral terminal, its associated busbar, or equivalent wiring, or both, shall have an ampacity equal to at least twice the ampacity of the largest ungrounded supply terminal.

Exception: Where portable switchboard equipment is specifically constructed and identified to be internally converted in the field, in an approved manner, from use with a balanced 3-phase, 4-wire with ground supply to a balanced single-phase, 3-wire with ground supply, the supply neutral terminal and its associated busbar, equivalent wiring, or both, shall have an ampacity equal to at least that of the largest ungrounded single-phase supply terminal.

(2) Supply Neutral. The power supply conductors for portable switchboards shall be sized considering the neutral as a current-carrying conductor. Where single-conductor feeder cables, not installed in raceways, are used on multiphase circuits, the grounded neutral conductor shall have an ampacity of at least 130 percent of the ungrounded circuit conductors feeding the portable switchboard.

So when I run my permanent wiring to the disconnect / Cam-loc location I only have to treat the neutral as a current carrying conductor.

When the roadie plugs into the Cam-loc their neutral shall have an ampacity of at least 130 percent of the ungrounded circuit conductors and the Neutral terminal and bus bar of the portable switchboard shall have an ampacity equal to at least twice the ampacity of the largest ungrounded supply terminal.

I guess the harmonics stop at the Cam-locs. [Linked Image]

Bob
Posted By: winnie Re: Neutral Current Carrrying? - 09/17/05 10:43 AM
Hmm. Which ampacity table is used for 'single-conductor cables, not installed in raceways' ?

-Jon
Posted By: iwire Re: Neutral Current Carrrying? - 09/17/05 10:54 AM
Jon

I do not know, the more I read 520 the more my head was spinning. [Linked Image]

I imagine 400.5 for cords.

Bob


[This message has been edited by iwire (edited 09-17-2005).]
Posted By: ShockMe77 Re: Neutral Current Carrrying? - 09/28/05 01:58 AM
If I could ask a quick question here...

Why is it important to not connect both ungrounded conductors to the same phase on a multi-branch circuit at the panel?

I kind of understand that the neutral will 'heat-up' but I'd like an explanation of why it would heat-up.

Thanks

--Ron
Posted By: gfretwell Re: Neutral Current Carrrying? - 09/28/05 03:25 AM
When you are on opposing phases the neutral current is only the unbalance of both sides (balanced current returns on the phases). If you are on the same phase neutral current is the sum of the phase currents.
Posted By: Roger Re: Neutral Current Carrrying? - 09/28/05 10:23 AM
Ron, look at the drawing below, notice how current adds on the grounded conductor, as Greg points out, when only one leg is used.

[Linked Image]

Now notice how only the unbalanced current is carried on the neutral when opposing legs are used.

[Linked Image]

Roger
Posted By: giddonah Re: Neutral Current Carrrying? - 09/29/05 07:24 PM
I could be wrong, and will probably get corrected if I am, but the two phases are 180 degrees apart. When one wave is passing along one particular point in the wire, it's hitting its maximum positive amplitude as the other phase is hitting its maximum negative amplitude. These two waves counter each other and cancel. IIRC it's superposition of waves. You can see this on a rope if two people try to send waves down the rope at the same time. In the middle of the rope, where the waves pass each other out of phase, the rope doesn't move.

let the corrections begin...
Posted By: iwire Re: Neutral Current Carrrying? - 09/29/05 07:35 PM
Sounds pretty good to me.
Posted By: Dnkldorf Re: Neutral Current Carrrying? - 09/29/05 08:27 PM
But what happens when the two phases are 120 degrees apart?


Dnk....
Posted By: iwire Re: Neutral Current Carrrying? - 09/29/05 08:40 PM
As in a using only 2 phases from a 3 phase supply?

Then they do not cancel each other out entirely.
Posted By: winnie Re: Neutral Current Carrrying? - 09/29/05 09:13 PM
I'd actually take this one step further: In a multi-wire branch circuit using two phases from a three phase wye supply, the current flowing into the shared neutral essentially doesn't cancel out.

Consider: a multi-wire branch circuit using all three phases could balance perfectly, if each is carrying the same current. This means that the current flow from any _single_ phase is somehow being balanced by the other two phases taken together. If you remove this third phase, then the current that flows into the neutral must be the same as the current that would flow in this third phase.

If you have a multi-wire branch circuit using two phases from a three phase wye supply, then you can calculate the current flow in each conductor, so here are a few examples:
HotA HotB Neutral
0 0 0
10 10 10
20 0 20
0 20 20
20 20 20
20 10 17.3 (this is the condition that minimized neutral current flow)

All of the above presume the same power factor on all loads; if this is not true, then you have different phase angles for the current flow, and different results. If you have a line to line load in the above example, then clearly you won't have any neutral current, but now the phase angles of the current flowing in HotA and HotB will be 180 degrees apart, even though the phase to neutral voltages are 120 degrees apart.

-Jon
Posted By: Dnkldorf Re: Neutral Current Carrrying? - 09/29/05 09:27 PM
Jon, I got to say I really enjoy your posts.
One of the best at explaining things here.

Thanks for taking the time.


Dnk........
Posted By: ShockMe77 Re: Neutral Current Carrrying? - 09/29/05 10:29 PM
Gfretwell, and Roger, thank you both for your explanations to my question. It is much appreciated.