200 amp feeders
-
06/03/05
11:12 AM
For a 200 amp residential service am I correct with 2/0 cu or 4/0 al thhn. the amprage on 2/0 is 195 thats why I am not sure.
Posted By:
Roger
Re: 200 amp feeders
-
06/03/05
11:59 AM
Nov, see 310.15(B)(6) and Table 310.15(B)(6), if you meet this criteria you are correct.
Roger
Posted By:
Active 1
Re: 200 amp feeders
-
06/03/05
02:44 PM
Don't forget to check with local codes. I don't know where your at but many places here require 3 #3ott CU.
Tom
©