Posted By: Electric Ian main lug or breaker for Sub Panel? - 04/02/05 02:35 AM
I am installing a sub panel in an attic space to be finished. It will be fed from a 60A breaker in the main panel in the basement. Would you typically use a main lug panel or main breaker panel for the sub in this situation ?
Posted By: Dave55 Re: main lug or breaker for Sub Panel? - 04/02/05 04:03 AM
I almost always use main breaker panels for sub-panels. I consider it an additional disconnect and haven't had any complaints from inspectors yet.

Dave
Posted By: Joey D Re: main lug or breaker for Sub Panel? - 04/02/05 06:49 PM
Most main breaker panels come with the neutral bar bonded to the ground bar or just have 2 neutral bars bonded together. This would need to be seperate in a sub panel use
Posted By: BobH Re: main lug or breaker for Sub Panel? - 04/02/05 08:05 PM
You should be able to do it either way as long as grounded conductor is isolated from grounding conductor and you use a 4 wire feeder.
Posted By: northstar Re: main lug or breaker for Sub Panel? - 04/02/05 10:55 PM
Im for the Main breaker panel with an Isolated nutreal bar. The added disconnect and protection could only be a good thing. However, the more economical way to go is the main lug which has an iso bar already in it.