Posted By: JakeJ1 Feeder Cable - 03/24/05 03:13 PM
Is there an allowance for a splice (inside a junction box) for a "Feeder Cable". The NEC doesn't seem to mention it one way or the other.
Posted By: manny Re: Feeder Cable - 04/01/05 09:06 PM
You are right, NEC doesn't say restriction for this, at least, I couldn't find it.
According to 110.14 (B), 215 and 300.13. But be carefull, some utility companies don't permit to do that before meters to avoid stealing energy.
Posted By: iwire Re: Feeder Cable - 04/01/05 09:53 PM
It would be very unusual for a power company to be concerned with feeders.

They concern themselves with service conductors.

The NEC does not prohibit splices in either.
Posted By: blackrd Re: Feeder Cable - 04/01/05 10:24 PM
Power utilitys also arent required to follow the NEC. They are governed by I believe the NESC(national electric suppliers code?)