when is a main breaker required for a sub panel????
Posted By: sparky Re: main breaker - 10/15/01 11:27 AM
smokey,
take a look at 384-16 [Linked Image]
Posted By: Redsy Re: main breaker - 10/15/01 11:35 AM
Main OC protection is required for "Lighting and Appliance" panelboards (see 384-14a for a description of lighting & appliance panelboards, see 384-14b for power panelboards), however, it need not be integral to the panel. The panel may be considered protected by the OC protection of the feeder supplying the panel.