Posted By: ameterguy Florescent fixture problem - 12/05/04 08:16 PM
I had an electrician install 5 2x2 troffer fixtures in my cellar drop ceilings, these use two u-shaped 34 watt bulbs. (The fixture are Liothonia lighting, sold at Home Depot.) The fixtures are on three different circuits, two circuits have two fixtures and the third circuit has one fixture.

The fixture are all acting up, delayed starting, up to 10 - 15 seconds or they do not come on at all. The electrician has checked the wiring and remade all the wiring connections, resat the bulbs, etc.

What should be checked next? What can I have my electrician do next?

Any help would be greatly appreciated

Bob
Posted By: NJ Wireman Re: Florescent fixture problem - 12/05/04 08:54 PM
Well lets see a couple of things.

#1 is the basement heated?

#2 Are the fixtures new or used?

#3 What else if anything is one each of the circuits?

#4Are the ballest humming or getting hot?
Posted By: Electric Eagle Re: Florescent fixture problem - 12/05/04 09:44 PM
Try new bulbs.
Check the grounding.
Are the correct bulbs being used? They make U shaped bulbs in T8 and T12?
Posted By: ameterguy Re: Florescent fixture problem - 12/05/04 11:01 PM
NJ Wireman,

The basement is heated.

The fixtures are new, been in use 3 - 4 wks.

The fixtures replaced the existing pullchain fixtures that were originally installed in the cellar ceiling, when the house was built. Two circuits are on bedroom receptical circuits and the third is on the living room receptical circuits.

The ballast are not humming, but they get a little warm. Electrician said that was normal.

Electric Eagle,
The Electrician verified the grounding at the fixtures and in all boxes all the way back to the panel. All was tight, but he replaced all connections anyway.

I verified the bulbs are correct, but I have not tried replacing them. I will try that this week.

Do you think the bulbs are the problem? Or could it be the ballasts? (I will try bulbs first, as there are cheaper.)

Bob
Posted By: mxslick Re: Florescent fixture problem - 12/05/04 11:15 PM
ameterguy:

If you're using the green-ended "eco-friendly" bulbs, that's most likely the problem. The very low mercury content makes them hard-starting. Replace 'em with standard tubes.
Posted By: watthead Re: Florescent fixture problem - 12/05/04 11:53 PM
Get some sylvania lamps. Call lithonia and tell them you heard that would solve the problem and see what they say. I am not usually not brand loyal on fluorescents, as any of the big three (GE,Philips,Sylvania) will do. In certian cases with the u-bends the sylvania just work better.
Posted By: NJwirenut Re: Florescent fixture problem - 12/06/04 12:04 AM
The U-bend bulbs usually have a foil tape strip that runs along the inside of the "U". If this strip is damaged or missing, the lamps can be hard starters. The strip should be grounded by contact with the retaining clip that holds the closed end of the "U".
Posted By: hbiss Re: Florescent fixture problem - 12/06/04 01:53 AM
Talked about this before. I pulled my hair out over this same problem. The solution was new lamps from a DIFFERENT manufacturer. The ones giving me problems were Phillips, brand new right out of TWO different cases. Problem went away with GE.

-Hal
Posted By: Electric Eagle Re: Florescent fixture problem - 12/06/04 02:03 AM
Thread Jack:
What do you guys do with your old tubes? Until recently I didn't know that they contain mercury so I just tossed them. Now I don't know what to do with them.
Posted By: kinetic Re: Florescent fixture problem - 12/06/04 05:17 AM
What do you do with the old ballasts as well? I never knew about either until recently but where are they supposed to end up?
Posted By: Trumpy Re: Florescent fixture problem - 12/06/04 07:47 AM
NJ_Wireman,
Good point Kenny.
The strip that is used on these tubes is there for good reason.
It's what we call an Earthed starting strip and it works in relation to the Grounded body of the fitting.
It requires the inductance of the gas fill in the lamp and the body of the fitting to strike the lamp.
Without this strip, starting currents can be horrendous and will lead to early failure of the fittings and lamps. [Linked Image]
Posted By: electure Re: Florescent fixture problem - 12/07/04 01:06 PM
I've found the same problem as Hal has, and it was with Phillips lamps, although quite a while ago. GE's were the fix.

Kinetic, Ballasts manufactured post-1979 are usually marked "No PCBs", and aren't considered to be hazmat. Anything that's not marked as such must be disposed of as hazmat. We call a licensed company for disposal.