Posted By: jayson size of wire? - 09/25/04 10:36 PM
what size of wire is service wire is needed for a 200 amp panel copper size? aluminum size?
Posted By: iwire Re: size of wire? - 09/25/04 10:39 PM
The smallest permitted would be 4/0 AL for a dwelling service
Posted By: Active 1 Re: size of wire? - 09/25/04 11:49 PM
We use 3/0 copper for all 3. Lots of locals want that. Someone elce might know the code but I think NEC lets you go one smaller?
Posted By: Joey D Re: size of wire? - 09/25/04 11:51 PM
2/0 copper
4/0 aluminum
Posted By: iwire Re: size of wire? - 09/25/04 11:54 PM
If we are talking dwelling unit services the NEC allows the use of Table 310.15(B)(6).

200 amp service 2/0 CU or 4/0 AL

100 amp service 4 CU or 2 AL

This does not apply to commercial services.

[This message has been edited by iwire (edited 09-25-2004).]
Posted By: jayson Re: size of wire? - 09/26/04 03:07 PM
thanks guys