I am bidding a service upgrade on a 4 family. I've done many houses and duplexes but this is a first. I checked Art.230, but Im still not clear and the local inspector isn't much help. The four meters & panels are grouped in the basement. Does anyone know if I need a disconnect or overcurrent protection on the service entrance conducors before I tap for the individual services?
[This message has been edited by REELECTRIC (edited 02-26-2004).]
We need a little more information. Where are the panels?
Are the panels installed, one in each apartment? Then you need a main disconnect and OCP for the building and main disconnects and OCP in each panel.
Are the panels grouped together in the basement? Then you don't need a main for the building, but you still need mains and OCP in each panel.
BTW, what is a man house? A singlr family?
Earl
"Man house" should have been many single family homes. A great typist I'm not, sorry. Disconnects are grouped in the basement. Thanks Earl.
REELECTRIC,
Welcome to ECN!
FYI, you can edit mistakes that you make by clicking on the
above the post where you made a mistake.
Bill
[This message has been edited by Bill Addiss (edited 02-26-2004).]
As long as it is fewer than six individual services, you shouldn't need a separate disconnect, IIRC. (barring unforseen local Code interpretations)
[aside] One concern is if there are common areas (laundry, storage, hallways, garage) an additional panel/meter might be needed for (terminology blank) "landlord provided power" for those areas. If there are, your customer (landlord) might want a separate meter and panel for those areas. Just a thought.[/aside]