Posted By: Attic Rat Bends in Conduit - 01/16/04 02:17 PM
..This is a question I've always had, and maybe,you guys could help me out...
Ok, I know that you can have no more than 360 degrees of conduit bending radius [352.26].,..but, is that in a single 10' section of pipe,..or the entire run..?
here's a hypothetical scenario...my 1" EMT exits the top of a CB panel only to turn 90 degrees, in the ceiling,then travel about 30' then 90 degree again,travel another 25' or so, take up (2) 45 degree offsets, then another 90 degree turn down the wall,where it 90 degrees again into a disconnect...I know that this run seems ridiculous,but I'm just trying to pose a "worse-case" scenario,for clarification of 352.26...any takers???
AR
Posted By: Big A Re: Bends in Conduit - 01/16/04 02:26 PM
Hey Rat,

I think it says that it is 360 degrees between runs, so as long as you put a pull point in there somwhere you are OK. (pull point being a conduit body or a box)
Posted By: Roger Re: Bends in Conduit - 01/16/04 02:27 PM
Attic Rat, the xxx.26 sections of all the conduit sections are worded as to between pull points at any distance, long or short.

This can be a C condulet installed in the run.

In your example you would be in violation.

Roger
Posted By: Attic Rat Re: Bends in Conduit - 01/16/04 02:41 PM
I'm sorry Roger, I don't quite follow you..with this part..
Quote
This can be a C condulet installed in the run.
..I guess the "ol' gray matter" is starting to get confused..sorry..
AR
Posted By: earlydean Re: Bends in Conduit - 01/16/04 02:49 PM
A "C" Condulet is a trade name for a conduit body. The "C" refers to the configuration. "C" Condulets have conduit openings on two opposite sides only, with access for pulling conductors on one side only. Think of a single device Bell box with only two threaded openings, top and bottom. Now streamline it, rounding the corners, and leaving no space for a device. That's a "C" Condulet.
Posted By: Attic Rat Re: Bends in Conduit - 01/16/04 02:59 PM
..I see, and inserting that in the run would satisfy the intent of 352.26 ?? in lieu of a splice box ...
Thanx everyone,
AR,..Russ

[This message has been edited by Attic Rat (edited 01-16-2004).]
Posted By: CRW Re: Bends in Conduit - 01/16/04 03:17 PM
A "C" fitting or condulet is just like an "LB" except straight, if you can picture that.
Posted By: resqcapt19 Re: Bends in Conduit - 01/16/04 04:15 PM
Don't forget that if the conductors are #4 or larger, that many standard "C" fittings do not comply with 314.28(A)(1).
Don
Posted By: Mean Gene Re: Bends in Conduit - 01/16/04 05:23 PM
Russ,
Sometimes a picture is worth a thousand words . . . [Linked Image from smartparts-usa.com]
Posted By: Attic Rat Re: Bends in Conduit - 01/17/04 12:59 AM
..Thanx Mean Gene!!!!!
Posted By: stamcon Re: Bends in Conduit - 01/17/04 01:20 AM
What's wrong with Rat's installation? 90+90+45+45+90=360
Posted By: Roger Re: Bends in Conduit - 01/17/04 01:24 AM
Stamcon, you made me read it again. [Linked Image]

You missed one 90.

Quote
my 1" EMT exits the top of a CB panel only to turn 90 degrees, in the ceiling,then travel about 30' then 90 degree again,travel another 25' or so, take up (2) 45 degree offsets, then another 90 degree turn down the wall,where it 90 degrees again into a disconnect

Roger
Posted By: stamcon Re: Bends in Conduit - 01/17/04 03:20 AM
oops....thanks Roger

steve