I Need Help Understanding? ( I MUST Stay Above 208v ) - 01/12/04 02:36 AM
Main Building Power
Single Phase 237v
The Equipment Electrical Requirements are:
208-228 3 Phase 60hz 7 KVA
We are using a 15 HP Rotary Phase Converter CNC
It Converts 230volt Single Phase to 230volt 3-Phase
I MEASURED THE POWER AT PHASE CONVERTERS PANEL
Under No Load Voltage Measured;
L1 to G = 118v
L2 to G = 119v
L3 to G = 205v
L1 to L2 = 236v
L2 to L3 = 237v
L3 to L1 = 235v
Under A Load
L1 to G = 117v ... "Changed -1 volt"
L2 to G = 119v ... "No Change"
L3 to G = 199v ... "Changed -6 volt"
L1 to L2 = 235v ... "Changed -1 volt"
L2 to L3 = 228v ... "Changed -9 volt"
L3 to L1 = 233v ... "Changed -2 volt"
Power then goes through a set of
SORGEL BUCK AND BOOST TRANSFORMERS
Square D Company (Transformer Catalog # 500SV43B) Two Transformers Required
.500 KVA
(Its to buck the voltage from 237 to 213v)
Then To Equipment (2 Color Press Hamada c248cx-sf)
Measured Power at Equipment Panel
Under No Load I Measured;
L1 to G = 109v
L2 to G = 108v
L3 to G = 204v (WHY?)
L1 to L2 = 213v
L2 to L3 = 211v
L3 to L1 = 214v
Under A Load
L1 to G = 109v ... "No Change"
L2 to G = 106v ... "Changed -2 volt" (WHY?)
L3 to G = 198v ... "Changed -6 volt" (WHY?)
L1 to L2 = 210v ... "Changed -3 volt" (WHY?)
L2 to L3 = 210v ... "Changed -2 volt" (WHY?)
L3 to L1 = 204v ... "Changed -10 volt" (WHY?)
I NEED TO STAY ABOVE 208v on all phases
Thank you for your INFO & HELP!
Single Phase 237v
The Equipment Electrical Requirements are:
208-228 3 Phase 60hz 7 KVA
We are using a 15 HP Rotary Phase Converter CNC
It Converts 230volt Single Phase to 230volt 3-Phase
I MEASURED THE POWER AT PHASE CONVERTERS PANEL
Under No Load Voltage Measured;
L1 to G = 118v
L2 to G = 119v
L3 to G = 205v
L1 to L2 = 236v
L2 to L3 = 237v
L3 to L1 = 235v
Under A Load
L1 to G = 117v ... "Changed -1 volt"
L2 to G = 119v ... "No Change"
L3 to G = 199v ... "Changed -6 volt"
L1 to L2 = 235v ... "Changed -1 volt"
L2 to L3 = 228v ... "Changed -9 volt"
L3 to L1 = 233v ... "Changed -2 volt"
Power then goes through a set of
SORGEL BUCK AND BOOST TRANSFORMERS
Square D Company (Transformer Catalog # 500SV43B) Two Transformers Required
.500 KVA
(Its to buck the voltage from 237 to 213v)
Then To Equipment (2 Color Press Hamada c248cx-sf)
Measured Power at Equipment Panel
Under No Load I Measured;
L1 to G = 109v
L2 to G = 108v
L3 to G = 204v (WHY?)
L1 to L2 = 213v
L2 to L3 = 211v
L3 to L1 = 214v
Under A Load
L1 to G = 109v ... "No Change"
L2 to G = 106v ... "Changed -2 volt" (WHY?)
L3 to G = 198v ... "Changed -6 volt" (WHY?)
L1 to L2 = 210v ... "Changed -3 volt" (WHY?)
L2 to L3 = 210v ... "Changed -2 volt" (WHY?)
L3 to L1 = 204v ... "Changed -10 volt" (WHY?)
I NEED TO STAY ABOVE 208v on all phases
Thank you for your INFO & HELP!