Posted By: Edward Cord connected spa?? Why not? - 01/10/04 06:32 AM
I was asked this question by a home owner
" why can't i use a cord and a end plug for my spa plug into a clothes dryers outlet whenever i want to use my spa?

Here is what i said.
" first the dryers outlet is not GFCI protected, Secondly it is not rated for 50Amps third the cord will creat trip hazard."

any other reasons you can think of?

Thanks
Posted By: Trumpy Re: Cord connected spa?? Why not? - 01/10/04 08:37 AM
Edward,
Putting a cord on a piece of equipment like this, would make it an appliance, no matter the current draw.
Considering that the thing is outdoors, would entail that it has GFCI protection as a minimum.
Posted By: Tom Re: Cord connected spa?? Why not? - 01/10/04 02:48 PM
Interesting. If the spa is located outdoors, cord & plug connections are allowed, but I've never seen a dryer receptacle installed outdoors.

Indoors, a cord & plug connection is allowed, but only at 20 amps or less. So this spa cannot be plugged into a dryer receptacle if the spa is located indoors. It needs a connection by a Chapter 3 wiring method.

Tom
Posted By: electricman2 Re: Cord connected spa?? Why not? - 01/10/04 03:25 PM
A dryer receptacle has no equipment ground. It is a 125/250V non-grounding receptacle. You are no longer allowed to use the neutral to ground equipment. The 3pole 4 wire grounding receptacle would have to be used.

[This message has been edited by electricman2 (edited 01-10-2004).]
Posted By: golf junkie Re: Cord connected spa?? Why not? - 01/10/04 03:47 PM
"Indoors, a cord & plug connection is allowed, but only at 20 amps or less"

Tom,
Where does this rule come from?
What about kitchen ranges? Cord & plug connection at 50-60 amps.

GJ
Posted By: Bill Addiss Re: Cord connected spa?? Why not? - 01/10/04 04:06 PM
Edward,

If it's inside 680.43 w/Exception says it can't be cord and plug connected over 20A

As the person installing it that's all I have to know.

Tom,

Have you seen many Outdoor cord-and-plug connected Hot Tubs?

Bill

[This message has been edited by Bill Addiss (edited 01-10-2004).]
Posted By: Edward Re: Cord connected spa?? Why not? - 01/10/04 05:00 PM
Thanks for your replies.

But home owner's main question is "may he do that Installation per code?"

I said NO.

Do you guys see other downside to this type of installation besides the one posted above.

The unit is outdoor the plug is indoor.


(Bill)
(Have you seen many Outdoor cord-and-plug connected Hot Tubs?)

Although you havn't seen any cord and plug connected spas, but is it allowed per NEC and is it a good idea?
Posted By: walrus Re: Cord connected spa?? Why not? - 01/10/04 05:29 PM
Lets say I'm going to install a hot tub indoors on a concrete slab. How do I get the wiring across the floor to the spa. A piece of SO seems like the best method but doesn't SO have to be in a cord set or can it hard wired with SO??
Posted By: sparky Re: Cord connected spa?? Why not? - 01/11/04 08:47 PM
per 680.42(Outdoor Installations)A spa or hot tub installed outdoors shall comply with the provisions of Parts I and II of this article, except as permitted in 680.42(A) and (B), that would otherwise apply to pools installed outdoors.

680.42(A)(2)..

(2) Cord-and-Plug Connections. Cord-and-plug connections with a cord not longer than 4.6 m (15 ft) shall be permitted where protected by a ground-fault circuit interrupter.

bold mine

this part is confusing as (correct me if i'm off) they are making reference to pool usage in section IV Spas and Hot Tubs
Posted By: cpalm1 Re: Cord connected spa?? Why not? - 01/12/04 12:57 AM
"Lets say I'm going to install a hot tub indoors on a concrete slab. How do I get the wiring across the floor to the spa. A piece of SO seems like the best method but doesn't SO have to be in a cord set or can it hard wired with SO??"

I'm not an electrician, and i don't know all the detail of the code, such as putting a cord on a spa, but it just sounds like a terrible idea.

to get power to the spa in the center of a contrete slab, you could rent (or hire someone with) a power breaker and chip out a grove in the floor, put a pipe in in and then fill it back up with concrete.

another option, since you say it is indoors would be to build a false pillar right next to the spa. the wiring could go up the center of the pillar and then go through the ceiling. you could mount hooks on the pillar for hanging towels and clothing for spa users.

For the post about plugging in the spa to a dryer outlet when you want to use it- Just tell the homeowner that besides the fact that it violates code, it will be very inconvenient. When you want to use the spa, you will have to plug it in a couple hours before you plan to use it so it can warm up. also, spas get really nasty if the water is not circulated frequently. if it was left unplugged for a 5 days or so, it will get NASTY no matter how many chemicals you put in it.
Posted By: Big Jim Re: Cord connected spa?? Why not? - 01/12/04 05:01 AM
Small cord and plug connected units do exist. I had one at my last house. 10' so cord with a gfi in a bell box in line and a 15A plug. with such low power, it needed to be connected all the time. For the bigger unit, I'm sure some building or fire code would not buy stringing such a cord through a door or window.
Posted By: PCBelarge Re: Cord connected spa?? Why not? - 01/12/04 12:02 PM
400.8(3)
Does not permit cords through doorways, windows or similar openings.

Pierre
Posted By: rlrct Re: Cord connected spa?? Why not? - 01/12/04 05:58 PM
walrus/cpalm1,

We have a room in our addition built specifically for a spa. The room has tile floors. I ran THWN in liquidtight flex from the spa to a box in the wall. In the box, the THWN is wire-nutted to 6/4 NM. The circuit itself is protected by a 50 amp GFCI, 2-pole breaker.

I ran that because I couldn't use a cord and plug connection. Otherwise, I would've just used a marine-grade, weatherproof 50 amp cord and plug set.

Rob
Posted By: Tom Re: Cord connected spa?? Why not? - 01/12/04 11:08 PM
Bill,

There is a dealer in my area selling package units for indoor/outdoor use that come factory wired with a cord, 120 volts , 20 amp circuit required. The unit is convertible to 240 & the instructions call for hard wiring, no cord at this voltage.

These units are sold this way so the happy owner can take it home & plug it in & enjoy. The joy ends when the weather turns cold & the heater won't keep up (it is a 240 volt heater being run on 120 volts).

Tom
Posted By: iwire Re: Cord connected spa?? Why not? - 01/12/04 11:27 PM
Wow this is all very confusing, I am glad I do not have to wire these I would be lost.

This further confuses me.
Quote
factory wired with a cord, 120 volts , 20 amp circuit required. The unit is convertible to 240 & the instructions call for hard wiring, no cord at this voltage.

I am missing the logic here, 120 or 240 still 120 volt to ground.

Why is one treated different from the other?