GFCI testing - 10/20/03 07:53 PM

If I replace a NEMA 1-15 receptacle with a 5-15 GFCI, will the test and reset buttons on the front work when the receptacle is properly wired?
Posted By: resqcapt19

Re: GFCI testing - 10/20/03 08:01 PM

Yes, but a plug in GFCI tester will not trip the device.