Posted By: Frank Cinker Service lateral conductors - 10/13/03 12:57 PM
Can service lateral conductors in raceway be installed in common trench with a waterline?
Posted By: Electric Eagle Re: Service lateral conductors - 10/13/03 01:52 PM
Unless local codes prohibit it and the proper burial depth can be met, it should be OK. So, check with the AHJ.
Posted By: triple Re: Service lateral conductors - 10/14/03 01:23 AM
Do you mean the service entrance conductors? Aren't service lateral conductors installed by the poco? Where are these wires going to and from?
Posted By: Frank Cinker Re: Service lateral conductors - 10/14/03 11:06 AM
Pad mounted transformer: 4000V-120/240V
We are to install the secondary raceway and conductors via trench to meter and service equipment
Posted By: amp-man Re: Service lateral conductors - 10/14/03 06:46 PM
triple,

In may area (N. Calif.), the builder is responsible for providing conduit for service lateral conductors (between xfrmr and meter). The utility co pulls in their conductors.

And in PG&E and SMUD territory, yes, a water line can share the trench with the power. Has to be 24" of separation.

Cliff