Posted By: feltch 20 amp lighting - 09/26/03 01:04 PM
I'm just wondering if it's possible to run a switched light off of a 20 amp circuit? Will the wiring inside the light fixture be sufficient? If it is possible do I use a 15 amp or 20 amp switch?
Posted By: ElectricAL Re: 20 amp lighting - 09/26/03 01:19 PM
That's a pretty wide open question. . .try to narrow the field a bit with the context for the luminaire. . .commercial or residential and is residential the use of the 20 amp circuit, wattage of the switched load.
Posted By: feltch Re: 20 amp lighting - 09/26/03 01:25 PM
This would be for residential use. The switch would be for a single light fixture 65 Watts.
Posted By: Ryan_J Re: 20 amp lighting - 09/26/03 01:48 PM
65 watts diveded by 120 volts equals about 1/2 of an Amp. I'm sure your wiring is rated for that.
Posted By: HotLine1 Re: 20 amp lighting - 09/26/03 07:18 PM
Yes, it's possible. Without starting a big debate over "tap rules", you should wire the fixture in #12 wire. The factory wiring within the fixture is satisfactory for the "load served". THe switch may be rated 15 amp, as it is only "switching" the 65 watt load of the fixture.

Please substitute the word "luminare" for "fixture" within the above comments, to be politically correct. It's hard for us guys that have been around for a while to "change our ways" on some subjects.

EDIT:

AS always, if you personally are "not qualified" to perform electrical work, you should consider locating a local electrical contractor/electrician. Residential voltages can cause serious bodily harm, and death as a worst case scenario.

John

[This message has been edited by HotLine1 (edited 09-26-2003).]
Posted By: George Re: 20 amp lighting - 09/26/03 11:28 PM
Hotline1 ---

permanent life support my be a "worser" case senerio.