Posted By: jimmyinanniston 400 amp service residential - 09/23/03 11:50 PM
when installing two 200 amp panels in paralell to a 400 amp meter base does the two 200 amp feeds need to be the same length? This is a residential application using ser and two 200amp disconects.
Posted By: PCBelarge Re: 400 amp service residential - 09/24/03 12:04 AM
Jimmy
Yes they should be the same length.

Pierre
Posted By: iwire Re: 400 amp service residential - 09/24/03 12:12 AM
Pierre I think he means two separate runs from the 400 amp meter to two separate 200 amp panels. Parallel but not parallel conductors as in 310.4

If this is whats happening they do not have to be the same length.

Jim are the conductors joined together at one end or both ends?

Bob

[This message has been edited by iwire (edited 09-23-2003).]
Posted By: jimmyinanniston Re: 400 amp service residential - 09/24/03 01:15 AM
yes 2 seperate runs to two seperate panels.
Posted By: iwire Re: 400 amp service residential - 09/24/03 02:01 AM
Jim in that case the run to one panel can be different from the other.

To be considered parallel conductors they would need to fit this description.

Quote
electrically joined at both ends to form a single conductor.

Bob
Posted By: SJT Re: 400 amp service residential - 09/24/03 06:55 PM
Would it be possible to run 4" into the basement, or have a weather proof trough, and from that run the 200 amp service feeders to the panels?
Then splice the 500's along with the 2/0's to the panels. Is coming off the bottom of a 400 amp meter with 2- 200 amp runs, allowed?
Posted By: ElectricAL Re: 400 amp service residential - 09/24/03 07:52 PM
That's a pretty expensive assembly, for the customer, compared to two runs of SER cable.