Can you legally install a dimmer on a half/hot wall receptacle? Code Section?
Posted By: resqcapt19 Re: Dimmer Usage - 06/15/03 03:31 AM
see 404.14(E)
Don
Posted By: alconems Re: Dimmer Usage - 06/15/03 03:39 AM
Maybe your in a diffrent book. There is no 404-14 in the 1999 NEC
Posted By: pauluk Re: Dimmer Usage - 06/15/03 12:43 PM
It's in the 2002 code with a new/changed mark beside it.

Quote
404.14 (E) Dimmer switches. General-use dimmer switches shall be used only to control permanently installed incandescent luminaires (lighting fixtures) unless listed for the control of other loads and installed accordingly.
Posted By: Hutch Re: Dimmer Usage - 06/15/03 08:27 PM
I understand the reasons for this restriction.

Is there any way around this using non-standard recepticals a la the UK's use of old standard BS 2A or 5A sockets for switched/dimmed table/bed-side lighting instead of standard 13A ones? Can non NEMA recepticals and plugs be used in the US, or must everything be explicitly 'listed' for use?
Posted By: alconems Re: Dimmer Usage - 06/23/03 12:21 AM
Thanks for the help. At least now I can confirm the conflict I was having is valid. A customer recently asked me to do this( not the first time) and I said no( as usual). Until now I could not find anything on the subject in the code book (1999) but knew it sounded like a bad idea. Its great to know there's a place to go for help......SO (humbly) THANKS EVERYONE