Posted By: Nagelec NEMA Type 7 enclosures - 06/09/03 07:32 AM
Is NEMA Type 7 enclosures are for indoor use only? Can any one please clarify this and give the NEC reference?
Posted By: Redsy Re: NEMA Type 7 enclosures - 06/09/03 11:02 AM
Type 7 Enclosures are"for use indoors in locations classified as Class 1 Group A,B,C, or D.
Crouse-Hinds will provide an optional neoprene o-ring-type gasket to make the enclosure raintight.
For example:
EJB junction boxes that are "Style C" are considered NEMA 3,4,7 & 9.
See 2002 catalog, page 126.
Posted By: Nagelec Re: NEMA Type 7 enclosures - 06/09/03 02:23 PM
Thank you Redsy.