Posted By: rayh78 halogen lights and fluke meter - 05/07/03 02:21 PM
2 questions please.
Have 3 halogen under counter fixtures hooked together. each fixture has 3 bulbs and a rocker switch for two levels of dimming. Fixtures from Lowes made by good earth lighting. Keep getting bad transformers, thier customer service will send new transformers but they say have had problems if they are on too much and built up heat. Trans is 115V in and output 11.5V 60 watt max for each. Question, can I delete transformers and cheap switches and get one transformer to replace the 3 seperate ones somewhere to mount in a remote box & power with a regular wall dimmer switch. Is this a good idea. would get different brand but like brass housing on the fixtures.
Also Used my digital fluke to test transformer but would not read the 11.5 volts, I guess because voltage so low. Had to use cheap analog radio shack $15.00 old one. Always used the cheap meters before because of size but not durable. Now it seems also more dependable does this sound right? Any recommendations on a small durable analog multimeter under $100.00 so dont need a backup to carry.
Sorry so long but thanks for any input.
Posted By: Bill Addiss Re: halogen lights and fluke meter - 05/07/03 02:34 PM
Ray,

What you ask can be done, but it is not a simple matter. Replacing the transformer is much easier.

As far as the Fluke Meter goes, you may have to change scales (?) but it certainly should work. I use mine all the time to check batteries and they're only 1-1/2 v

Bill
Posted By: zapped208 Re: halogen lights and fluke meter - 05/07/03 10:22 PM
Ray & Bill,- you will not get a true reading with a digital meter testing the output of an electronic transformer.
Posted By: rayh78 Re: halogen lights and fluke meter - 05/07/03 10:36 PM
Any suggestions on a good small multimeter.
I did try my fluke T5 -1000 and you are right it will read a 1.5 volt DC battery at 2 volts but you still have to wait about 5 seconds for it to read. But it would not read at all the 11.5 volt AC.
Posted By: rayh78 Re: halogen lights and fluke meter - 05/07/03 10:38 PM
Also dont understand why these are so popular. I did not spend this kind of money on a meter to have to carry a backup analog one because I cant trust the fluke..
Posted By: elektrikguy Re: halogen lights and fluke meter - 05/07/03 10:57 PM
ray: I have done some installations for friends that involve undercounter task lighting. The little puck fixtures that I chose were line voltage fixtures with 120 G7 lamps I believe. I have not had a problem nor have any of the people had a problem. I realize that you have an existing condition but may save you some hassle in future.Hope this helps.
Posted By: Electricmanscott Re: halogen lights and fluke meter - 05/07/03 11:46 PM
If you can't have the lights on too long because heat will kill the transformer why have them at all. I would get my money back pronto! Buy a good quality UNDERCABINET (not undercounter) fixture from a lighting supplier.
Posted By: caselec Re: halogen lights and fluke meter - 05/08/03 12:27 AM
elektrikguy,

Were these 120V pucks part of a fixture or individual pucks? The 120V individual pucks are required to be surface mounted and plugged into a receptacle.

Curt
Posted By: elektrikguy Re: halogen lights and fluke meter - 05/08/03 01:42 AM
Yes they were individual lights. Each time I cut a new switch into wall and mounted a hidden receptacle under the CABINETS(Thanks Electricmanscott, thanks for pointing out honest typo. I am pretty sure I didn't mislead anyone into installing under the counter top.You are a lifesaver).
Posted By: Trumpy Re: halogen lights and fluke meter - 05/08/03 05:42 AM
Ray,
Are these electronic transformers that you are talking about?.
They must have a Load attached to them before you can measure thier output voltage. [Linked Image]
Posted By: seeks Re: halogen lights and fluke meter - 05/08/03 01:35 PM
Just a quick note - you cannot use a "regular" dimmer. - must have one rated for use with a magnetic transformer - this is a lesson learned the hard way!! Dimmer was $60.00!!! Also, this could be the cause of heat build-up in the transformer.
BTW - watch out for voltage drop. 12 volt systems like this dont allow you much wire length-typically approx. 10 feet using #12 AWG wire. Transformer will have to be centrally located and close to fixtures.