ECN Forum
Posted By: ga.sparky56 Earth voltage - 05/06/03 02:09 AM
The question: If I drive 2 ground rods,say 100' apart and put a meter lead on each one,will I get a voltage reading? Why or why not? Then you can thrash me for not knowing!
Posted By: Bjarney Re: Earth voltage - 05/06/03 03:12 AM
Two guesses… If the rods are of different metals, the two combined with soil moisture could form an electrochemical cell [battery] giving a low DC voltage. If there is a utility-distribution multigrounded neutral in the area, it may be possible to read some 60Hz voltage, like measuring taps on an energized resistor.
Posted By: George Corron Re: Earth voltage - 05/06/03 04:06 AM
If you use a galvanometer, you would have some luck. The concept of earth as a large electric sponge is a myth, especially now days with the utility neutral mentioned above, RF, etc..

Galvanometers can be made easily, hard to calibrate a home made though. I have one on my earth resistance meter, and it never fails to surprise me what comes from the ground...... OK, maybe the term is scares me.

I guess the answer is with a real sensitive meter, probably. BTW, rural is no protection, the worst I ever saw was in a VERY rural (I'll tell ya how rural, even Sparky66wv would think he was in the woods [Linked Image] )location with an earth return neutral..... dang near ruined my meter.
Posted By: Bjarney Re: Earth voltage - 05/06/03 05:23 AM
About a year ago there was a thread about "S.W.E.R."
https://www.electrical-contractor.net/ubb/Forum1/HTML/001230.html

This would probably give driven rods a little higher readings.
Posted By: wocolt Re: Earth voltage - 05/06/03 12:16 PM
I would think it would be very possible to read voltage between the two rods, aganin as mentioned depending where you are.
Part of the problem is the utility's grounding the primary neutral to the secondary neutral as the loads increase on the secondary side of the transformer the neutral current from the primary will increase to carry the load. It will apear on the secondary side because of the grounding.
For some reason farms have a much bigger problem with this than cities do.
Another thing is our system of grounding we go to the water pipe and Now drive two ground rods. At this point depending on the relative size of resistance the neutral return current will take these alternate pathes back to the transformer/source, creating Objectionable current on our system. I am not sure when they started grounding the systems but as it is we are standing on 1/2 of the circuit that is the neutral.
I am not saying it is a bad system but like anything else it has its flukes and this is one of them.

WmnColt
© ECN Electrical Forums