Posted By: renosteinke Inspection Foibles - 05/19/16 03:05 AM
My experiences with the inspection community have been generally professional, even positive. Yet, the current job has introduced me to a particularly vexing sort of inspector.

Mind you, this gent is professional in his manner, and seems to mean well. The problem is, well, he's rather limited in his exposure. Here are some of the matters we've had extensive conversations over:

1) Support of EMT. Specifically, where it passes through light steel framing. I've been using some plastic "mickey mouse" bushings, the same ones used by the plumber. This has led to quite a discussion about whether the pieces need to be UL listed for use with conduit. Last we spoke, he was still puzzled on the NEC's failure to require supports to be listed;

2) Grounding pigtails. Or, specifically, the use of ordinary wire nuts to connect them together, rather than using the "greenies." I'm not sure he can understand the UL explanation I provided;

3) The use of colored tape to identify larger wires as to phase and voltage. He has the opinion that if colored wire is made, we're supposed to use it. This particular issue has not been a problem for me- but I was shocked to hear him express that sentiment;

4) He expects MC used for 277 circuits to have the outer jacket marked with "480 volt" wire colors. Heaven forbid we use use black wire MC as a lighting whip on a brown circuit - but he'd never notice brown MC on a 'yellow circuit;' and,

5) Our use of stranded MC has him completely confused, as he's never seen it before. Since we're using it for the low-voltage side of LED lighting, he has unfortunately decided it's for low-voltage only.

So far, he's been more amusing than annoying. Have you ever encountered such an interesting inspector?
Posted By: twh Re: Inspection Foibles - 05/19/16 05:09 AM
I haven't had problems with inexperienced inspectors. I have had problems with certain types of inspectors.

It seems some inspectors look for a reason to allow what you do and others look for a reason to disallow it. The first doesn't want to use the power he has and the other might be willing to make up a reason to use it.

I have noticed that the harsh inspectors are hard on their co-workers, too. Sometimes inspectors have to cover for each other - like for holidays. When they cover a harsh inspector's area, they can't answer questions because they will be contradicted when he returns.

So, all my examples come from one inspector.

1) After checking my calculations, the inspector said that 90.25 is not greater than 90.

2) He made another electrician pull his cables out of an MCC and install a steel plate because he didn't think the top of the MCC was thick enough to prove a good ground connection to the connectors.

3) He made an electrician put anti-shorts in teck cable that had the rubber sheath around the conductors.

4) He made me go back to a job and strap another electrician's cables where they ran into a panel because I ran a cable into the same panel and I should have strapped theirs the way I strapped mine.
Posted By: gfretwell Re: Inspection Foibles - 05/19/16 07:01 AM
All I can say is some people are just wrong. I also understand some of them will refuse to admit it.
Reno's guy really sounds like he needs a little more education or a different occupation.
I have seen guys like this get beat up pretty bad at an IAEI meeting and I just hope they learned something. Some were inspectors who had been in the business for years.

... and yes, I have been wrong but I backed off and apologized when we looked in the code book.

Posted By: HotLine1 Re: Inspection Foibles - 05/19/16 08:38 PM
I agree 100% with Greg. I'm human.
Could I be incorrect? Yes!
Last week, I failed a panel change in a townhouse. N&G not separated. Units have a MCB at the exterior meters.

Ooop! This unit was not like the others. The meter was back to back with the panel. I spoke to the EC and apologized, and called the HO to do the same.

As to 'horror stories'; I'll add a guy who red tagged a Carlon gray Plastic old work device box that was NOT BONDED.

After two red tags, and to move the small job along, I drilled, tapped, and installed a ground pigtail. DUMB move?
I did not want to hold the job up any longer.

The guy never saw a gray plastic, deep old work device box!
He passed the rough, and life went on. This was at least 15 -20 years ago. Sometimes you can't win!


Posted By: renosteinke Re: Inspection Foibles - 05/22/16 01:58 PM
With some time to reflect ....

I suspect that there are two things that contribute to these situations.

First, there is the tendency these days for inspectors to be 'school trained,' to the exclusion of any real trade experience. Look at the job postings; they ask for certification, education, degrees - and are not interested in any actual trade experience.

Indeed, there's a tendency to start a new inspector off in something completely unrelated to any trade; they start as 'sign inspectors' or 'code enforcement.'

Second, well, the abuse of power always finds its' way into the right hands. The ability to strut around, to be the absolute authority, to appoint yourself king, attracts all the wrong sorts.

Indeed, the way you're treated as royalty, the way the dynamics of the relationship shield you from any accountability, almost force the inspector to develop an overly high opinion of himself.

The last factor is one that applies across the board: what passes for 'critical thinking' these days would confound Socrates.

Let's look, as an example, at those plastic supports I mentioned. These are substantial plastic bushings that wrap around the pipe, gripping it on all sides. There are two 'ears' that allow you to attach it to a metal stud:

http://www.homedepot.com/p/SharkBit...pension-Clamp-10-Pack-23071A10/202032968

Now, If I saw one of these wrapped around the pipe at every point where it passed through a stud, I would think "that's a pretty substantial support."

Our inspection troll instead thinks "I've never seen that use before. Surely it can't be right. I wonder if they're rated for that specific use? Where does it say these CAN be used? Aren't I the eagle-eye for spotting this
innovation! (And innovation is suspect, if not outright bad)."
Posted By: gfretwell Re: Inspection Foibles - 05/22/16 05:42 PM
I think "education" should also be telling you what the code is silent on. Exactly how you "support" equipment is one of those things. Certainly there are products made for the electrical trade that will hold up a piece of pipe but that may not be the best product for it. Plumbing pipes are actually a lot heavier than raceways because they are typically full of water and they may "hammer".
Posted By: HotLine1 Re: Inspection Foibles - 05/23/16 12:27 AM
Reno:
First, the hanger for the pex pipe would not raise my eyebrow, except to ask 'where did you find that?'
At $4.95 for 10 pcs. (from your link), I would not expect to see all that many!

Second, your comments on those that are 'book smart' and may lack 'hands on trade experience'. No argument on this from me! Yes, there seems to be a trend for 'multi-license' inspectors within the help wanted ads. Bldg/Fire. and Bldg/Plumb are common, along with the Administration Lic.

The following comment, may create an issue.....
" Second, well, the abuse of power always finds its' way into the right hands. The ability to strut around, to be the absolute authority, to appoint yourself king, attracts all the wrong sorts."

"Indeed, the way you're treated as royalty, the way the dynamics of the relationship shield you from any accountability, almost force the inspector to develop an overly high opinion of himself."

"The last factor is one that applies across the board: what passes for 'critical thinking' these days would confound Socrates."

To this I will say......

Yes, there may be some who go over the lines, but, to infer that it applies to all is not a fact that you cannot substantiate.


Posted By: ghost307 Re: Inspection Foibles - 05/23/16 01:52 PM
I can deal with most profession Inspectors that work for the various municipalities and jurisdictions. I generally find that working with them instead of butting heads goes a long way. Most times I can win them over and we can have a win/win discussion about what the intent of the requirements are...and I'm not above making a change if it's a low-cost way of getting out of a squirrely situation. Sometimes I need to go over their head; it generally works but it also sours any chance of a future peaceful coexistence.

My major issue with the vast majority of 'Home Inspectors' is that they compare everything to the standards of the most recent edition. I think if they were inspecting a log cabin in a frontier recreation town they would cite it for lack of GFCI receptacles.
Posted By: HotLine1 Re: Inspection Foibles - 05/23/16 01:58 PM
Ghost:

"Home Inspectors" are another breed that I (and most other State Lic. Inspectors) do not include within our profession.

Another story for another thread??

Posted By: ghost307 Re: Inspection Foibles - 05/23/16 05:53 PM
Agreed.
There are probably enough 'Home Inspector' stories around to start a whole 'nother website.
Posted By: renosteinke Re: Inspection Foibles - 05/24/16 05:51 AM
I just posted that link to show you what the support I mentioned looked like. They're not the exact supports I use.

Mine come in bags of 100, are sized to steel / copper pipe sizes, and are most often seen supporting HVAC line sets. They're available at plumbing houses, HVAC houses, and even my local Graybar branch (for 1/2" only). The price is more like 12 cents apiece.

As a way to keep pipe from rattling in steel studs, they're hard to beat.
Posted By: HotLine1 Re: Inspection Foibles - 05/24/16 02:11 PM
Reno:
As I said, the supports would not raise my eyebrows.

Thru phone calls from ECs and other inspectors, I have heard a lot of 'what the (insert your choice) is he talking about??'

Does a sleeve have to be UL listed? Guy used scrap pcs of 'Fire Red' PVC sprinkler pipe for sleeves. Another used scrap DWV.

Support methods? Let's not even go there now. Yes, there are 'some' who go to extreme reasoning, but is that because there is a lot of time on their hands?

Posted By: poorboy Re: Inspection Foibles - 05/24/16 07:27 PM
My boss was always kinda tight about buying certain items, one being 4 squares with brackets or Caddy H23 mounting brackets for use on steel stud jobs. We were told to use 1/2"X#8 tek screws thru the two tiny holes near the front on the side.

This was no picnic, as the holes were too small and you were really in need of three hands to do it quickly. Lots of bad language floated around during several consecutive all day "boxing sessions" on large jobs.

Along came a new inspector. He said those holes were not allowed to be used for mounting. We could not prove otherwise (what else would they be for?) but we workers then had all the authority we needed to tell the boss "Stop carrying 88 cents a box on your takeoffs and get us Caddy H23 brackets or side bracketed 4 sqs."

I loved that inspector, right or wrong, and the quality of the job was improved. All future jobs were much easier as well.

What had actually caused the inspector to question it was the way those of us who wanted a tighter mount screwed one tek screw back thru the stud into the side of the box creating a pointed "hazard" inside the box. You do what you have to to be satisfied with your mechanical soundness.


Posted By: HotLine1 Re: Inspection Foibles - 05/24/16 08:24 PM
Poorboy:

Just an FYI regarding the side holes in 4" square box.

Steel City Accessory item 52171-OW

'Add-on' ears to make a 4" sq 'old work box'

Check it out on Steel City website.

Posted By: gfretwell Re: Inspection Foibles - 05/24/16 11:15 PM
I have seen green ground screws in those holes. I was never sure if it was legal but I didn't fail them because the wire seemed secure. The boxed were tap conned to a block wall so the back holes were unavailable.
Posted By: HotLine1 Re: Inspection Foibles - 05/25/16 02:09 AM
I have not come upon the green screws, or anyone using the holes to mount the box either.

I don't think the green screw would bother me. A great idea from the box mfg's is the dimpled location for the green screw. Saves a lot of 'ooops'.