Posted By: big lug stapling romex - 01/29/03 04:09 AM
How far apart do you staple romex. I'm rewiring my house and was needing some advice. Thanks in advance.
Posted By: iwire Re: stapling romex - 01/29/03 04:15 AM
Within 12" of the box and every 54" after that.

2002 NEC 334.30
Posted By: sparky Re: stapling romex - 01/29/03 11:12 AM
code aside,
i staple (insulated) single runs loosley, at every 2' or so. anything more than 2 runs and i use stackers.

the intervention of 'other trades' has intimidated me to this point.
Posted By: Redsy Re: stapling romex - 01/29/03 01:00 PM
Keep in mind...
If you are using single-gang non-metallic boxes without internal clamps, you have to staple it within 8" of the box. 314.17 (C) ex. I like the stackers also. They make for a nice looking installation.

[This message has been edited by Redsy (edited 01-29-2003).]
Posted By: spyder Re: stapling romex - 01/30/03 12:35 AM
the minimums are with 8" of a NM box without clamps or 12" from a box with clamps and every 4 1/2 fett there after. Never staple on a twist, keep romex flat.

I once had a helper that could not grasp this concept so we had to go to stapling "hammer length apart", I kid you not...
Posted By: George Re: stapling romex - 01/30/03 01:54 AM
4' works nicely with usual stud spacing and plywood sizes.