Has anyone heard the phrase, "This is a comercial/industrial installation. You can't use #14 ga wire here. It has to be #12 ga minimum."?
Posted By:
HotLine1
Re: Comercial installs
-
10/21/11
03:56 AM
ONLY...if that verbage is within the job specs. Common trade practice is 12 for comm, but it's not code.
Posted By:
Tesla
Re: Comercial installs
-
10/21/11
04:05 AM
That phrase embodies the California Electrical Code.
Words to that effect rule here.
#14 is restricted to control circuits and residential installations.
Posted By:
Niko
Re: Comercial installs
-
10/21/11
07:19 AM
Originally Posted by Tesla
That phrase embodies the California Electrical Code.
Words to that effect rule here.
#14 is restricted to control circuits and residential installations.
I looked in the CEC 2010 but couldn't find this. Do you have a code section, because it is good information to have.