Posted By: cgw Panelboard vs. Loadcenter - 12/26/10 07:01 PM
What do you think of using a load center in lieu of a regular panelboard? This may be a matter of opinion?
By loadcenter I mean a Square D QO or similar. By panelboard I mean a Square D NQOD or similar.
A specific situation - a 200 amp 42 space house panel in a small apartment building?
Posted By: gfretwell Re: Panelboard vs. Loadcenter - 12/26/10 08:48 PM
Are you just talking about the difference between using an integral main breaker or a back fed main in the rails?
The biggest difference is how many slots you have available after you put in the breaker. It will usually take up 8 of you slots.
The other option you have with the Square D NQOD is bolt in breakers. It seems to be available either way.
Posted By: wa2ise Re: Panelboard vs. Loadcenter - 12/26/10 08:49 PM
That for the entire building? That would mean that the landlord will pay the power bill, I didn't think they did that anymore. Usually each tenant has their own meter and panel.
Posted By: KJay Re: Panelboard vs. Loadcenter - 12/26/10 10:05 PM
A load center would be less money. If the NQOD panelboards and bolt-on QOB cb’s aren’t specified in the plans, why you couldn’t use something else?
Posted By: JBD Re: Panelboard vs. Loadcenter - 12/26/10 11:03 PM
As far as UL and the NEC care, this is no difference between a panelboard and a load center.

For your installation, the only major differences include:
Load centers are designed to fit inside of stud cavities so they are about 3-1/2" d and 14"w. Panelboards cabineets are usually 5-3/4"d and 20"w.

Loadcenters breakers are normally plug-in style while panelboards are more often, but not always (i.e. NQB), bolt-in style.

Posted By: Steve Miller Re: Panelboard vs. Loadcenter - 12/27/10 01:20 AM
The NQOD gives you more space (in the form of depth) for the stuff they'll call you to add later. The real question is who's paying for it? NQOD is a lot more, especially if you use the bolt ins.
Posted By: Obsaleet Re: Panelboard vs. Loadcenter - 12/27/10 02:39 AM
Steve,
I prefer the panelboard in this situation. Unless you have space considerations. If you have a contract w/sq D and they are on it, they can be quite cost effective. I usally use the qo snap in cb but you could use the bolt on its a nice option. More room is better in my opinion.

Ob
Posted By: cgw Re: Panelboard vs. Loadcenter - 12/27/10 04:34 PM
I'm just looking for reasons to not use a load center.
Usually I would use a panelboard unless there were just a few circuits or I had to fit it in a 2X4 stud wall.
In this case though it is for the house loads in a very small (10 unit) senior apartment building and is single phase. On the other hand it is pretty full (about 37 circuits).