ECN Forum

Redundant ground

Posted By: VBSELECTRIC1

Redundant ground - 10/04/09 07:58 PM

Can some one explain what is Redundant grounding
Posted By: gfretwell

Re: Redundant ground - 10/04/09 08:46 PM

The term is used in article 517 (patient care areas) it generally refers to an additional grounding conductor.
They require a properly made up metallic wiring method (your ground) plus an insulated grounding wire (the redundant ground).
Posted By: McClarysElectric

Re: Redundant ground - 10/05/09 02:50 AM

Keep in mind the first EGC can be your conduit, then a properly sized insulated EGC inside.